    Refrigerant Recovery R404a



    Hi guys, I'm a new member so please be easy on me.

    I'm new to the industry and looking for some information.

    I have a blast freezer bitzer compressor to change out, I'm thinking all I need to do is shut the service valves and recover the vapour inside. Now all i have worked on is recovering R404a in a liquid state, no problem. But now I'm recovering in a vapour state, do I turn the recovery machine on vapour setting and connect my hoses to the liquid valve still on the recovery bottle? (Or vapour) as I'm guessing I want the refrigerant to go into the bottle in a liquid state?

    Sorry if this is a stupid question, but I would really like to know the correct method

    Thanks in advance



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Refrigerant Recovery R404a

    .

    It does'nt matter too much which valve you put it into the cylinder.
    I alway put it in through the liquid port because I always draw liquid
    out and it saves messing round with the bottle adapters and such.

    As for your machine if it has both a liquid and a vapour setting, then yes
    pull it out in the vapour and push it into the cylinder through any port,
    like I said I always use the liquid side of the cylinder anyway.

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Sep 2016
    Location
    Scotland
    Posts
    22
    Rep Power
    0

    Re: Refrigerant Recovery R404a

    Hi Rob,

    Appreciate the quick reply and info.

    One more question, does the recovery unit act as a condenser to change it from a vapour state to a liquid state?

    Cheers

  4. #4
    Join Date
    Sep 2016
    Location
    Australia
    Posts
    1
    Rep Power
    0

    Re: Refrigerant Recovery R404a

    Hi everyone,
    I m sorry i can not find own to create my own post... (it s the first time I use a forum in my all life...)

    anyway,

    I want to buy an ice cream machine to do some street ice cream but apparently the gas is R404A and I will use the machine outside with a temperature around 50degres... I saw than it could be dangerous to use the R404A in that temperature condition... and I don t want to risk to have any trouble or play with a potential bomb......

    could you please let me know what could be the gas able to hit -40/-45 degrees and able to run with a environmental temperature around 50 degrees?

    thx in advance for your understanding.

  5. #5
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Refrigerant Recovery R404a

    Quote Originally Posted by KegSalad View Post
    Hi Rob,

    Appreciate the quick reply and info.

    One more question, does the recovery unit act as a condenser to change it from a vapour state to a liquid state?

    Cheers

    Most recovery machines have a condenser on them and
    they try their best to turn the recovered refrigerant into
    a liquid.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  6. #6
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Refrigerant Recovery R404a

    Quote Originally Posted by KegSalad View Post
    One more question, does the recovery unit act as a condenser to change it from a vapour state to a liquid state?
    Cheers
    Another trick, if you are recovering any vast amounts of vapour, is to cool the recovery cylinder whilst you are reclaiming. Normally we do this by having a trickle of water on to the cylinder ensuring it is wet and acting as an evaporative cooler, otherwise as you push the hot vapour/liquid in to the cylinder it will get warm and this will slow down your recovery progress.


  7. #7
    Join Date
    Sep 2016
    Location
    Scotland
    Posts
    22
    Rep Power
    0

    Re: Refrigerant Recovery R404a

    Nice one, thanks for the information guys you've cleared that up for me!

    You learn something new everyday

    Cheers

  8. #8
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Refrigerant Recovery R404a

    If you are just seeking to empty the compressor of refrigerant to enable replacement, recover the refrigerant into the receiver, no need for a recovery cylinder then.
    Mostly found in Oxfordshire, UK :)

  9. #9
    Join Date
    Sep 2016
    Location
    Scotland
    Posts
    22
    Rep Power
    0

    Re: Refrigerant Recovery R404a

    Also got to change out the single PRV's on the water cooled condenser to duel PRV's. It's has a standby unit with a common receiver so need to keep the other system running while changing this out.

    When going to charge back into the system, do you use the recovery unit to pump the liquid back in once the pressure has equalised from the recovery cylinder?

  10. #10
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Refrigerant Recovery R404a

    Yeah, pump it back in with the reco machine.
    Mostly found in Oxfordshire, UK :)

  11. #11
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: Refrigerant Recovery R404a

    Why not just use a well vacced out recovery cylinder,shut off the service valves and let the vapour transfer to the cylinder?

  12. #12
    Join Date
    Sep 2016
    Location
    Scotland
    Posts
    22
    Rep Power
    0

    Re: Refrigerant Recovery R404a

    I thought R400 series refrigerant had to be recovered/charged in liquid form?

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Refrigerant Recovery R404a

    Quote Originally Posted by KegSalad View Post
    I thought R400 series refrigerant had to be recovered/charged in liquid form?
    Charged as liquid and recovered in any state, as long as you ensuring that all recovered refrigerant will be returned to system.
    Reason is fractionation. If you recover and recharge all refrigerant then there is no fractionation no matter of liquid or gas state of refrigerant.
    Last edited by nike123; 11-09-2016 at 11:13 AM.

  14. #14
    Join Date
    Sep 2016
    Location
    Scotland
    Posts
    22
    Rep Power
    0

    Re: Refrigerant Recovery R404a

    Thanks for that, I understand now how recovery and charging works now.

    It's much appreciated all your help

    Cheers guys

  15. #15
    Join Date
    Sep 2016
    Location
    Spain
    Age
    38
    Posts
    13
    Rep Power
    0

    Re: Refrigerant Recovery R404a

    Quote Originally Posted by cadwaladr View Post
    Why not just use a well vacced out recovery cylinder,shut off the service valves and let the vapour transfer to the cylinder?
    Wouldn't you need the recovery machine anyway to finish recovering all the gas? It would be a good start tho.

  16. #16
    Join Date
    Oct 2010
    Location
    Australia
    Posts
    88
    Rep Power
    15

    Re: Refrigerant Recovery R404a

    Quote Originally Posted by el_donks View Post
    Wouldn't you need the recovery machine anyway to finish recovering all the gas? It would be a good start tho.
    You *could* pack the recovery cylinder in a cooler full of dry ice and methylated spirit. No reco machine needed

    Yes it's a dirty hack, but great for recovering from nasty burnout a without putting that grunge through your reco machine.

  17. #17
    Join Date
    Sep 2016
    Location
    Spain
    Age
    38
    Posts
    13
    Rep Power
    0

    Re: Refrigerant Recovery R404a

    Sure, problem comes with big setups/large gas quantity