    Daikin VRV 4



    Evening all.

    Does anyone know how to re-auto address these systems? The BS5 reset button isn't on these like on the earlier systems.

    Cheers

    Eggs



  2. #2
    Join Date
    Mar 2009
    Location
    Uk
    Age
    41
    Posts
    121
    Rep Power
    17

    Re: Daikin VRV 4

    Push and hold reset button for 10 seconds or longer

  3. #3
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Daikin VRV 4

    Thanks Neddy

    As originally posted, on the VRV4 the reset button doesn't exist.

    Cheers

  4. #4
    Join Date
    Nov 2008
    Location
    scunny!
    Age
    35
    Posts
    302
    Rep Power
    22

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin VRV 4

    Not quite sure yet eggs with the new VRV4 but on the old units, if you press and hold the 'Mode' button for 20 secs it resets the unit back to factory condition. Worth a try.

  6. #6
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Daikin VRV 4

    Frank

    Daikin tech talked my guy on site through it. Apparently it involved pressing a button, I kid you not. Eighty eight yes 88 times to factory reset the thing ��
    All sorted now and running sweet as a nut.

    Cheers

    Eggs

  7. #7
    Join Date
    Mar 2009
    Location
    Uk
    Age
    41
    Posts
    121
    Rep Power
    17

    Re: Daikin VRV 4

    Sorry eggs, for some reason I typed reset instead of return.I'm sure it's the return button for 10 seconds or longer as I had to do it before. I've never heard of pressing a button 88 times. That is mental! Daikin should get rid of that binary!

  8. #8
    Join Date
    Mar 2014
    Location
    England
    Posts
    32
    Rep Power
    0

    Re: Daikin VRV 4

    Quote Originally Posted by Neddy View Post
    Sorry eggs, for some reason I typed reset instead of return.I'm sure it's the return button for 10 seconds or longer as I had to do it before. I've never heard of pressing a button 88 times. That is mental! Daikin should get rid of that binary!
    The 88 times to to set for short test run operation, other wise it'll carry out full test function from factory and most engineers don't have the patience, including me!

    Yes return will reset the search