Results 1 to 11 of 11
Thread: Hitecsa txv?
    Jul 2016
    Manchester
    7
    Hitecsa txv?
    Hi this is my first post and have been working on a system I am not familiar with at all. The system is running ok in heating but when switching over to cooling it then suddenly goes into vac and cuts out within seconds. 4 way valve has been changed and the only thing that I can see which looks like it could be a TXV is this picture attached any help or advice much appreciated
    Sep 2003
    ISRAEL
    66
    4,152
    38
    Re: Hitecsa txv?
    This is not a TXV. Its a pressure control.
    Jul 2016
    Manchester
    7
    Re: Hitecsa txv?
    Thank you, I thought as much just wanted to make sure as could not find a TXV anywhere on the system so had to second guess. Any ideas why it is going into vac once in cooling? Cheers
    ireland
    48
    1,308
    34
    Re: Hitecsa txv?
    Cooling expansion valve is most likely blocked, track your liquid line to the evaporator, maybe it is a piston type which will look like a flare nut?
    70
    10,627
    52
    Re: Hitecsa txv?
    Is the new 4 way valve operating correctly?
    Jul 2016
    Manchester
    7
    Re: Hitecsa txv?
    Yeah the new 4 way valve is working efficiently this was my first port of call and installed the new one today still no luck
    70
    10,627
    52
    Re: Hitecsa txv?
    Get a service manual from the manufacturers so that you can identify the circuit parts.
    ireland
    48
    1,308
    34
    Re: Hitecsa txv?
    was the system doing the same thing before replacing the 4 way valve?
    Jul 2016
    Manchester
    7
    Re: Hitecsa txv?
    Quote Originally Posted by al View Post
    Hi, yeah doesn't seem to have changed at all with the new one :/
    Jul 2016
    Manchester
    7
    Re: Hitecsa txv?
    I've looked for info everywhere on the web but with them being Spanish it's impossible to read and can't find anything associated with the model and with it being at least ten years old don't think I'll have much look
    Aug 2004
    45
    746
    Re: Hitecsa txv?
    Try CDL in Warrington or Hushon. We have bought Hitecsa from both in the past. They may be able to help. I have a couple of manuals in pdf. Ping me your email and i'll send them to you.
    Can't see much having changed over 10 years as they are quite prehistoric.
    Eggs