    Alternatives to R407C on low temperature system?



    Hi,

    We have a customer who have a new provision plant running on R407C. It has several freezer rooms on the same compressor and a fairly long pipe routing (40 meters), so the superheat is fairly high. I have measured discharge temperatures on the compressor top to 125°C (approx 260°F). How much higher is it inside the compressor?

    What would be a good refrigerant substitute? R407F - will it have lower discharge temp? Same capacity?

    What about R448A or R449A? How are discharge temp and capacity compared to R407C? Can the same expansion valves be used?

    Any other alternatives, without having to change liquid and suction line?



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Alternatives to R407C on low temperature system?

    407f or 507.

    40 meters is very bad design.

  3. #3
    Join Date
    Jun 2016
    Location
    US
    Age
    84
    Posts
    2
    Rep Power
    0

    Re: Alternatives to R407C on low temperature system?

    Hi,
    Thanks for the reply.

    507 is not an option. It will be banned soon in Europe. Need better GWP values for this new system.

  4. #4
    Join Date
    Mar 2010
    Location
    Lisbon
    Posts
    55
    Rep Power
    17

    Re: Alternatives to R407C on low temperature system?

    I do not have direct experience but according to the informations of the manufacturers, R448A or R449A may have a lower discharge temperature comparing with R407C or R407F. I think the diference is not much.
    Maybe a controled liquid injection system could solve the high discharge temperature problem...
    In the HFC world when the GWP reduces normaly the discharge temperature increases...

  5. #5
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: Alternatives to R407C on low temperature system?

    Quote Originally Posted by Mr.Nacogdoches View Post
    Hi,
    Thanks for the reply.

    507 is not an option. It will be banned soon in Europe. Need better GWP values for this new system.
    You are right. I would use the HFO R449A (it is not a HFC). This refrigerant doesn't have so high discharge temperature as the (R22) and R407F. With (R22) and R407F you need extra cooling to the compressor. But with R449A it's almost as the R404A/R507 which only at part loads and lower suction pressures combined with high discharge pressures you need a extra cooling with refrigerant (CIC system), or water or fan forced air at the compressor heads.
    To make progress is never good enough, I want to do better and better and better

  6. #6
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: Alternatives to R407C on low temperature system?

    Quote Originally Posted by chemi-cool View Post
    407f or 507.

    40 meters is very bad design.

    40 meters it's "what is it". Some plants have the machine room next to the services others not. Sometimes there is cold stores at 60...100 meters of pipe running between the cold stores and the machine room.

    Of course we have to count with suction pressure loss increasing or not the nominal diameter.

    In the current thread if you the superheat is very high at the compressor suction inlet so open a little more the expansion valve...so the aircooler will give a little more capacity and the compressor will say "thank you" » lower discharge temperature and increased capacity.
    To make progress is never good enough, I want to do better and better and better

  7. #7
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Alternatives to R407C on low temperature system?

    When there a too long lines, a cap tube between liquid line and suction line near the compressor, SV controlled can do wonders to extend compressor life.