    Smile parallel and series condenser



    Hi All,

    I am designing a condensing unit for the industrial air-con. I have a 7 hp compressor with the cooling capacity 19kW and 2 condenser each with 8kW heat rejection capacity.

    I have a doubt whether connect the condenser in series or parallel to get more cooling capacity.
    kindly request you guide me to design the most efficient one. Thank you



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: parallel and series condenser

    Check your figures first as heat of rejection does not add up to refrig capacity plus heat of compression/ motor drawn Kws.

  3. #3
    Join Date
    Sep 2016
    Location
    Singapore
    Age
    33
    Posts
    3
    Rep Power
    0

    Re: parallel and series condenser

    Thanks for you kind reply,
    The heat rejection of the compressor is 4.2 kW, So total heat needed to rejected from the condensers is 4.2 + 19 = 23.2 kW.

    I understand that I can not achieve this 23.2kW Using my condensers. Please let me know series or parallel connection will be efficient.

  4. #4
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14

    Re: parallel and series condenser

    Using parallel scheme it would give you an adnvantage over the cold months of year.

  5. #5
    Join Date
    Sep 2016
    Location
    Singapore
    Age
    33
    Posts
    3
    Rep Power
    0

    Re: parallel and series condenser

    Thanks for your information. Here the ambient temperature is around 30C all over the year. Is there any advantage in series scheme?

  6. #6
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: parallel and series condenser

    Hi, Thanu

    Welcome to RE forums ... it will be nice to start here
    http://www.refrigeration-engineer.co...p?72-New-to-RE
    to introduce yourself to us ... but you can do it at anytime ...

    Quote Originally Posted by Thanu View Post
    Thanks for your information. Here the ambient temperature is around 30C all over the year. Is there any advantage in series scheme?

    check here:
    http://docuk.download/allpdf/handboo...ne-stamper.pdf

    or read this ...

    https://books.google.hr/books?id=G47...ration&f=false

    ... hope this will help you ...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  7. #7
    Join Date
    Mar 2010
    Location
    Lisbon
    Posts
    55
    Rep Power
    17

    Re: parallel and series condenser

    As a general rule you will have best results with paralel condensers but you will have to be careful with the piping design. Check the recomendations, for example
    http://www.evapco.eu/sites/evapco.eu...131-e_0706.pdf

  8. #8
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: parallel and series condenser

    It will work but for a short while.
    Calculated heat rejection is 23.2kw, you need at least 25kw condenser.
    you did not mentioned what refrigerant you use which might require even bigger condenser.
    With what you got and your determination to have a go any way, I bring you a few lines from the immortal book "Alice in wonderland.

    `"Cheshire Puss,' she began, rather timidly, as she did not at all know whether it would like the name: however, it only grinned a little wider. `Come, it's pleased so far,' thought Alice, and she went on. `Would you tell me, please, which way I ought to go from here?'

    `That depends a good deal on where you want to get to,' said the Cat.

    `I don't much care where--' said Alice.

    `Then it doesn't matter which way you go,' said the Cat."

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •