    Post Need help in designing flooded evaporator



    We need some help in designing a flooded evaporator with R404A. Cooling capacity of 3-5 T. Specifically need help with oil management and return of oil to the compressor.

    Anyone has experience with such a system? Any pointers will be appreciated.

    -Infi



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Need help in designing flooded evaporator

    Hi infi.
    I inherited a low temp R22 gravity fed evaporator and surge vessel system, a raging/ constant problem recovering oil floating on top of refrigerant, particularly at -40SST the oil turned to honey consistency. the system had hot gas driven skimmers from operating level, giant waste of time.
    The system should of had several stages of oil separators after compressor to eliminate any oil carry over.
    The only way I could clear oil out was a total pump out, allow time time get oil fluid then drain it off manually. R22 and R404a have similar characteristics. magoo.

  3. #3
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Need help in designing flooded evaporator

    Hi infi
    Firstly don't use R404A in a flooded system, use R507 . Fit oil separator ,and an Oil Rectifier .
    The Rectifier samples refrigerant from the evaporator , this refrigerant/ oil is then lead into a rectifier pot which has a small heater inside. The heater then boils the refrigerant out of the oil and is vented to suction leaving pure oil in the pot. the oil is then fed to the compressor via a float valve on the compressor sump

  4. #4
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Need help in designing flooded evaporator

    hi
    could you draw the diagram please ?

  5. #5
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,035
    Blog Entries
    4
    Rep Power
    31

    Re: Need help in designing flooded evaporator

    Infi,

    I have commissioned a few freezing system with R-404a in south america where we used an oil rectifier.
    these were liquid overfeed systems where we used pumps to pump liquid from a LP receiver to the evaporators.

    You don't give us too much information on how the system around the evaporator is designed, if it's liquid overfeed with pumps, I can give you two ways to get very good oil return
    -Cheers-