    50hz-60hz



    Guys.
    what are the pros or cons(if any) if say a 50 HZ (cycle) compressor is run on a 60 HZ (cycle) system and vice versa? with the comp. being rated for only one cycle and not both?



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: 50hz-60hz

    It will give +/- 20 % cooling capacity, it will pull more current, it will wear faster, it will make more noise.

    I think almost any 50 HZ compressor can run on 50 Hz. This will give no serious problems als long as you stay under max allowable current.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: 50hz-60hz

    We fitted some 60hz fans some years ago (240V) and they burnt out in a very short time.

    We also had some York condensing units imported to the UK, via France, where the wiring was "upgraded" to comply with CE certification. We had enormous problems with these units as the cam timers continually burnt out as they were 60 hz. Even the replacements supplied by York were 60 hz so the problems just went on and on.

    It appears that 60 hz equipment causes the motor to run faster creating more heat which eventualy destroys the motor.

    If you apply the formula for motor speed (RPM = 60*hz/pole pairs - friction factor) then for a 50 hz supply we get 60 x 50 /2 (for a 4 pole motor) - 4% = 1440 RPM

    If you apply the same motor to a 60hz supply you get 1728RPM - an increase of 20.16%.

    Hope this helps.

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: 50hz-60hz

    With compressors, you have an increased massflow, so the compressor will cool enough.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    nico sonico's Avatar
    nico sonico Guest

    Re: 50hz-60hz

    hi!
    i have also tha same problem, we have a water chiller design 400v, 50hz: but our supply here is 440v, 60hz so we have to change the primary transformer and the pump motor that will fit in 440v 60hz, is it will couse problem with the whole unit, how thus affect the cooling system of the chiller,,

    thanks
    nico sonico

  6. #6
    Join Date
    Oct 2001
    Location
    New Jersey
    Age
    71
    Posts
    83
    Rep Power
    0

    Re: 50hz-60hz

    Hey guys, here in the US the 50 hz thing is a problem with motors. We had a machine quite a few years back that was from Italy I believe. Most of the motors we had to have rewound. The only 50 hz motors that were successful thoughout the machine's existence were the ones that did not run constantly....they were pulsed for short periods of time. It was a very long ordeal with the motorshop and a lot of heartache. Interesting what Peter had mentioned about the cooling effect. I have done that with large transformers....keep them cool and the capacity can be increased.

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: 50hz-60hz

    keep them cool and the capacity can be increased.
    A little bit like cooling a CPU then and increasing the computing speed?

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: 50hz-60hz

    Quote Originally Posted by Robearbam
    ...keep them cool and the capacity can be increased
    The same thing happens to fan motors in cold storage. The motor amps increase due to the higher air density, so in effect you are getting higher output from the motors. The cold air provides sufficient cooling from cooking the motors.

Similar Threads

  1. 110v 60hz in a country w/ 220v 50hz
    By dkupinsky in forum Technical Speculations
    Replies: 22
    Last Post: 02-08-2010, 03:20 PM
  2. 50HZ compressor on a 60HZ circuit
    By dan wong in forum Technical Speculations
    Replies: 28
    Last Post: 13-06-2009, 05:52 PM
  3. 60Hz Copeland scroll compressor
    By Lc_shi in forum Fundamentals
    Replies: 5
    Last Post: 05-06-2006, 09:08 PM
  4. Looking for 60hz appli in UK
    By nilechamp in forum Domestic
    Replies: 3
    Last Post: 27-01-2006, 09:40 AM
  5. 50Hz vs. 60Hz, okay to run at slower frequency?
    By pezagent in forum Commercial
    Replies: 10
    Last Post: 26-05-2003, 07:48 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •