    daikin u4 fault



    system details RZQ71B9V3B1 CONNECTED TO TWO FFQ35B8VIB Cassetts

    Age 10 yrs

    After about 8hrs running the system goes into U4 fault, when in U4 fault one of the fan coil fans runs.

    service history no faults system serviced twice yr from new

    When in fault LED lights on cassettes flash

    Green LED GH HAP on condensing unit flashes

    have disconnected terminal three from condensing unit and disconnected terminal three from both fan coil, there was a 1.9dcv on first fan coil and a 2.1dcv on fan coil two.

    there is no external condense pump fitted to this system.

    Help needed please

    David

    [Edit - thread moved from 'refrigerants' as it was not the topic of this post.]
    Last edited by Brian_UK; 22-08-2016 at 10:48 PM.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: daikin u4 fault

    Have you checked the interconnecting wiring?

    There may be a defective indoor pcb.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: daikin u4 fault

    Is terminal 3 only connected on one indoor unit, not both? used to be the case on other brands.
    Mostly found in the southern part of this green and pleasant land.

  4. #4
    Join Date
    Aug 2014
    Location
    Australia
    Age
    36
    Posts
    68
    Rep Power
    10

    Re: daikin u4 fault

    I would also check the fan motor. Sometimes a faulty fan motor can cause a U4 fault.
    Unplug it and start the unit, See if it runs ok for a little bit then it will fault out on fan motor missing fault. If U4 occurs then you may still have a faulty indoor PCB or interconnects