    AHU tripping on the control panel



    Hi everyone
    I have a ahu tripping on the control panel..... I reset it and start it up and it works fine for 15 mins or so then just trips again.... Any ideas? I suspect it to be the fam motor but it spins fine and seems weird how it takes 15 mins to trip.

    Thanks dan



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: AHU tripping on the control panel

    Did you check the amp draw and does it fit the over load settings?

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: AHU tripping on the control panel

    Running overcurrent or the overload is failing.

    Monitor the running current, check that all ahu access doors are closed.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Aug 2016
    Location
    Uk
    Age
    37
    Posts
    23
    Rep Power
    0

    Re: AHU tripping on the control panel

    I havent checked the running current as i didnt have my testers on me at the time. I know all the protective devices are correct as its been there for years. All doors are closed. Would there be any reasons for the running current to suddenly increase when it's been running for a while?
    I will check the draw and running current tomorrow.

  5. #5
    Join Date
    Nov 2008
    Location
    scunny!
    Age
    35
    Posts
    302
    Rep Power
    22

    Re: AHU tripping on the control panel

    does it have a fan speed contoller

  6. #6
    Join Date
    Aug 2016
    Location
    Uk
    Age
    37
    Posts
    23
    Rep Power
    0

    Re: AHU tripping on the control panel

    No unfortunately not

  7. #7
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: AHU tripping on the control panel

    Quote Originally Posted by danielc4514 View Post
    I havent checked the running current as i didnt have my testers on me at the time. I know all the protective devices are correct as its been there for years.


    Overload devices goes weak with time, causing them to trip at lower currents than they are adjusted to and marked for.
    Electrical cables and terminations looses continuity with old age.
    Electrical motors get worn with age and change their characteristics.
    Fan belts get worn and change the loadings on the motors.
    Fan scrolls get blocked and change the loadings on the motor.
    Fire dampers closes.

    Good engineering practices dictates that running currents are verified and over load devices re-calibrated as part of routine maintenance.

    But then again, we just assume that it is an over current device tripping... It might as well be a thermal cut out or a flow control device or...


  8. #8
    Join Date
    Nov 2010
    Location
    wales
    Posts
    54
    Rep Power
    15

    Re: AHU tripping on the control panel

    Would the high ambient be a cause? Is the condenser really clean? Higher head pressure results in higher running amps. Just something to check if its been ok up till last few days.

  9. #9
    Join Date
    Aug 2016
    Location
    Uk
    Age
    37
    Posts
    23
    Rep Power
    0

    Re: AHU tripping on the control panel

    Quote Originally Posted by The Viking View Post


    Overload devices goes weak with time, causing them to trip at lower currents than they are adjusted to and marked for.
    Electrical cables and terminations looses continuity with old age.
    Electrical motors get worn with age and change their characteristics.
    Fan belts get worn and change the loadings on the motors.
    Fan scrolls get blocked and change the loadings on the motor.
    Fire dampers closes.

    Good engineering practices dictates that running currents are verified and over load devices re-calibrated as part of routine maintenance.

    But then again, we just assume that it is an over current device tripping... It might as well be a thermal cut out or a flow control device or...

    Thanks for that, very informative. So today i checked the running current and it was 7.8 amps and the protective device was set at 6, after listening carefully you can hear the bearings are going. New fan motor it is then.

    Thanks all for taking time to help ��

  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: AHU tripping on the control panel

    Glad you've found it and thanks for letting us know.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    601
    Rep Power
    28

    Re: AHU tripping on the control panel

    Good work.
    Just a thought or 2;

    If it's a belt driven fan, also check your belt tension and the fan bearings.
    Also check the pulleys. I've replaced a lot over the years that have got worn out, often to the point where putting tension on the belt causes the pulleys to literally chew it due to pinching.