    weak compressor or blockage system



    Hi
    i got split ac unit
    classic type
    24000 BTU
    rotary compressor
    capillary tube system
    R22 refrigerant
    it had leak due to damage suction line pipe
    so i replaced

    made deep vacuum
    charged system by weight
    i installed the system

    after 1 hour of operation discharge line iced
    and suction pressure was 35 psi
    and no cool

    current for the system is 13
    and draw amperage was 9 amp
    voltage was 215 volt

    then what i did
    i thought my weight charge was non correct
    so i added more refrigerant
    suction press reached 65 psi
    and amp draw reached 13
    which rise gradually until it reached 15 so compressor overloaded
    is that blockage or bad compressor


    Power consists not in being able to strike another but in being able to control oneself when anger arises

  2. #2
    Join Date
    Mar 2014
    Location
    Australia
    Posts
    36
    Rep Power
    0

    Re: weak compressor or blockage system

    Hi Kefah
    Have you tried a pump down test on the compressor?
    As far as a blockage is concerned checking Superheat and Subccoling will assist in diagnosing.

  3. #3
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: weak compressor or blockage system

    i did this to charge outdoor unit only by weight
    i closed the discharge and attched manifold to suction
    and started compressor
    when system sucked 1.900 kg as in name plate
    i closed suction line
    and switched off unit


    ok if pump down done then i have blockage and compressor ok??
    Power consists not in being able to strike another but in being able to control oneself when anger arises

  4. #4
    Join Date
    Mar 2014
    Location
    Australia
    Posts
    36
    Rep Power
    0

    Re: weak compressor or blockage system

    The basic health checks would be compressor pump down to 0psi. If you can achieve this then the compressor is most likely ok.
    Superheat (aim for 6k as you would already know)
    Sub cooling (if high then blockage, check capillary, blocked drier etc)
    Also check non condensables. Assuming fans, coils etc are clean and working ok. You mentioned you replaced the suction line. Was it an identical size? How did the original one fail?

  5. #5
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: weak compressor or blockage system

    Kefah

    Your compressor sounds ok, if it wasnt pumping properly then your liquid line wouldnt be iced up, sounds like the drier might be blocked.

    recover your gas and change the drier, flush some nitrogen through the outdoor and indoor units in case of capillary blockage and vacuum and recharge.
    Mostly found in the southern part of this green and pleasant land.

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: weak compressor or blockage system

    There is no driers in most split system AC units!
    Only filter!

    If compressor curent is 80% or less than on nameplate, compressor is probably inefficient! But that is case only if everything else is fine.

    Check my blog entry:
    http://www.refrigeration-engineer.co...ling-scenarios

    "discharge line" in split system is part of evaporator , since it is after capillary. It is filed with gas-liquid mixture of certain "quality". Mixture is present because of pressure drop in capillary and phase change of refrigerant occurred by heat energy spent to cool down liquid refrigerant to saturation temperature of refrigerant at that point (phase change energy). That doesn't necessary mean that you have any restriction.

    First check air flow across evaporator with air flow meter, and if evaporator is clean from any dirt. Than charge by weight.
    Than measure compressor current at max fan speed. If current is within 80-100% then measure superheat.

    Low room temperature and low humidity and low air flow can be cause of smaller diameter pipe icing as well as evaporator icing.

    Quality could be found and understood by looking at Pressure Enthalpy Chart for that refrigerant.
    Last edited by nike123; 07-08-2016 at 04:46 PM.

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: weak compressor or blockage system

    Quote Originally Posted by Airsteve View Post
    Superheat (aim for 6k as you would already know)
    Superheat with capillary tube as expansion device is variable and not constant!
    Therefore, charging by weight is easiest and only secure way to properly charge system and to eliminate improper charge as probable cause!
    Last edited by nike123; 07-08-2016 at 05:05 PM.

  8. #8
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: weak compressor or blockage system

    evap is clean
    room is very hot
    charged by weight
    fan speed is max and ok
    Power consists not in being able to strike another but in being able to control oneself when anger arises

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: weak compressor or blockage system

    But that doesn't mean that air flow is correct. You should measure it to be sure.
    Than check for supply pipe collapsing at bends and (filter-drier, if present) blockage by moisture (heat portion of pipe where it start icing by hot gun).

    From your first post, and if we asume that above is correct, than we have this scenario:
    MILD RESTRICTION (factory charge) = High superheat. Low suction pressure, indoor TD & current draw. Normal to high subcooling. Normal to low head pressure
    Last edited by nike123; 07-08-2016 at 04:58 PM.

  10. #10
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: weak compressor or blockage system

    thank u all
    for very useful info
    80% its blockage in filter or capillary
    Power consists not in being able to strike another but in being able to control oneself when anger arises

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: weak compressor or blockage system

    Could be moisture, vax or oxidation if brazed without nitrogen.
    Check with hot gun at point where icing start, but only after proper charging by weight.
    If cappilary is cold to touch at beginig, than it is filter blockage!
    Last edited by nike123; 07-08-2016 at 05:10 PM.

  12. #12
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: weak compressor or blockage system

    ok
    i will check then reply u
    Power consists not in being able to strike another but in being able to control oneself when anger arises