09-05-2006, 04:13 AM #1
accumulator
Hello forum users
I wonder if the accumulator can be used in the system which involves TXV and receiver-direr without causing operational problems. My knowledge is that the accumulator is only used with the capillary tube not with TXV. Any help is greatly appreciated. Thank you
best regards
-
09-05-2006, 07:25 AM #2
Re: accumulator
hi mohammed
the suction accumulator is used with tev systems
it give stability to system and constant suction pressure
regards
-
09-05-2006, 08:04 AM #3
Re: accumulator
Hi afeef
Thank u for ur kind reply. However, my experience is that the TXV regulates the refrigerant flow correspondingly to the imposed cooling load on the system by adjusting the degree of superheat. Thereby, the TXV ensures that the refrigerant will be passed to the compressor is almost 100% dry. Therefore, the accumulator is not negated in this case and will be effective only during the existence of capillary tube, correct me if i am wrong. Regarding to the action of its function as absorber for moisture and to remove debris from the system, this role is taken by the receiver-drier which is necessary to be installed with TXV. So now all the roles of the accumulator are already accomplished by TXV and receiver-drier. In addition, the system does not need the accumulator in this case unless it is necessitated more protection for the compressor from ref. liquid with taking into account the more suction side pressure drop. Enlighten me if it is not true.
Best regards
-
09-05-2006, 08:21 AM #4
Re: accumulator
hi mohammed
you are right about the purpose of accumulator.
i find the accumultor instauled with tev system , also it instauled in capllary systems
thanks for explanation
good day
-
09-05-2006, 09:09 AM #5
Re: accumulator
Thank you afeef. Have a nice day .
my regards
-
10-05-2006, 02:08 AM #6
Re: accumulator
Hi Mohamed
My knowledge is that the accumulator is only used with the capillary tube not with TXV. Any help is greatly appreciated. Thank you
On heat pumps and simple hot gas defrost systems, they are there to provide a safety tank for unevaporated refrigerant that has been switched to travel back down the suction line from the evaporator.
With low temperature refrigeration systems, iced up coils occur often enough to permit the exansion valves to overfeed and flood back to the compressors.
Accumulators are not without their drawbacks. They are often made of steel and will rust through. They can plug the oil return oririfice and starve the compressor of oil. And finally... just how large should the accumulator be?
-
10-05-2006, 04:21 AM #7
Re: accumulator
Hi Mohammed
Suction line accumulators are just for added protection, if coils ice or your evaporator fans trip trip you run the risk of getting liquid refrigerant back to the compressor.
Accumulators are selected by the by the system capicty @the deign SST
-
10-05-2006, 04:47 AM #8
Re: accumulator
Hi Dan
Thank you so much for wealthy information and good explanation.
regrads
-
10-05-2006, 04:53 AM #9
Re: accumulator
Hi Julian
Thanks for your clarification of accumulator purpose
-
10-05-2006, 06:42 AM #10
Re: accumulator
Originally Posted by Dan
I agree completely. Although, a good service tech should purge with N2 while braising so there should be nothing in the system to block the oil return orifice.
Unless there has been a burnout where the burnout dryer should be place prior to the suction accumulator. As for "rusting"? If it is installed in a location where the system is prone to corosion I'd sujest giving it a coat of Kirby coat or Kill rust to be ultra safe. Will only cost you 50cents for that piece of mind. You would usually find a CPR valve after the accum. where there is H/G defrost. Applications with H/G defost in my opinion MUST have an accumulator.
-
10-05-2006, 09:02 PM #11
Re: accumulator
Applications with H/G defost in my opinion MUST have an accumulator.
Our friend M.O'b queried this stating that it was not necessary.
Any comments anyone??
-
10-05-2006, 09:22 PM #12
Re: accumulator
My experience with TXV's and refrigeration systems is one where I suggest an accumulator on any system. Sooner or later the system will exhibit some behavior where someone will wish they had installed one before the compressor went to pieces.
It is simply cheap insurance for a lot of problems that can and do occur. Of course for some, the problem is simply being cheap and saving the upfront cost of the accumulator.
Indeed, for hot gas systems the potential for liquid flood back is much higher and I would agree with the previous statement.
-
12-05-2006, 09:14 PM #13
Re: accumulator
Originally Posted by frank
Me I use an accumulator
Kind Regards, AndyIf you can't fix it leave it that no one else will:rolleyes:
-
12-05-2006, 10:00 PM #14
Re: accumulator
HI Andy,
Those Thermobank units were some of the first ones I found that were built without accumulators. And as usual they should have been supplied by the factory.
Later versions are provided.
Did not make for a very happy customer I can tell you.
Similar Threads
-
DX v/s Gravity
By Hemant Anand in forum IndustrialReplies: 7Last Post: 19-07-2006, 02:16 AM -
Bearing trouble - rotary compressor
By rosetennis in forum Industrial CompressorsReplies: 6Last Post: 18-05-2006, 01:26 AM -
suction accumulator selection
By Lc_shi in forum FundamentalsReplies: 9Last Post: 26-04-2006, 02:29 PM -
Frost on the suction line
By lana in forum Trouble ShootingReplies: 19Last Post: 22-01-2006, 06:04 AM -
Suction Line Accumulator
By bersaga in forum CommercialReplies: 11Last Post: 26-05-2003, 10:48 PM