    accumulator



    Hello forum users

    I wonder if the accumulator can be used in the system which involves TXV and receiver-direr without causing operational problems. My knowledge is that the accumulator is only used with the capillary tube not with TXV. Any help is greatly appreciated. Thank you

    best regards



  2. #2
    Join Date
    Aug 2005
    Location
    iraq
    Age
    67
    Posts
    130
    Rep Power
    19

    Re: accumulator

    hi mohammed
    the suction accumulator is used with tev systems
    it give stability to system and constant suction pressure
    regards

  3. #3
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: accumulator

    Hi afeef

    Thank u for ur kind reply. However, my experience is that the TXV regulates the refrigerant flow correspondingly to the imposed cooling load on the system by adjusting the degree of superheat. Thereby, the TXV ensures that the refrigerant will be passed to the compressor is almost 100% dry. Therefore, the accumulator is not negated in this case and will be effective only during the existence of capillary tube, correct me if i am wrong. Regarding to the action of its function as absorber for moisture and to remove debris from the system, this role is taken by the receiver-drier which is necessary to be installed with TXV. So now all the roles of the accumulator are already accomplished by TXV and receiver-drier. In addition, the system does not need the accumulator in this case unless it is necessitated more protection for the compressor from ref. liquid with taking into account the more suction side pressure drop. Enlighten me if it is not true.

    Best regards

  4. #4
    Join Date
    Aug 2005
    Location
    iraq
    Age
    67
    Posts
    130
    Rep Power
    19

    Re: accumulator

    hi mohammed
    you are right about the purpose of accumulator.
    i find the accumultor instauled with tev system , also it instauled in capllary systems
    thanks for explanation
    good day

  5. #5
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: accumulator

    Thank you afeef. Have a nice day .

    my regards

  6. #6
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: accumulator

    Hi Mohamed

    My knowledge is that the accumulator is only used with the capillary tube not with TXV. Any help is greatly appreciated. Thank you
    Accumulators are used very often with TXV systems. Especially in refrigeration systems. I cannot say that I wholeheartedly agree with their use, but I can provide some rationals.

    On heat pumps and simple hot gas defrost systems, they are there to provide a safety tank for unevaporated refrigerant that has been switched to travel back down the suction line from the evaporator.

    With low temperature refrigeration systems, iced up coils occur often enough to permit the exansion valves to overfeed and flood back to the compressors.

    Accumulators are not without their drawbacks. They are often made of steel and will rust through. They can plug the oil return oririfice and starve the compressor of oil. And finally... just how large should the accumulator be?

  7. #7
    Join Date
    Apr 2005
    Location
    Adelaide
    Age
    54
    Posts
    10
    Rep Power
    0

    Re: accumulator

    Hi Mohammed

    Suction line accumulators are just for added protection, if coils ice or your evaporator fans trip trip you run the risk of getting liquid refrigerant back to the compressor.

    Accumulators are selected by the by the system capicty @the deign SST

  8. #8
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: accumulator

    Hi Dan
    Thank you so much for wealthy information and good explanation.

    regrads

  9. #9
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: accumulator

    Hi Julian
    Thanks for your clarification of accumulator purpose

  10. #10
    Join Date
    Oct 2005
    Location
    In a 2 bedroom unit. Why's That? :)
    Posts
    314
    Rep Power
    19

    Re: accumulator

    Quote Originally Posted by Dan
    Hi Mohamed



    Accumulators are used very often with TXV systems. Especially in refrigeration systems. I cannot say that I wholeheartedly agree with their use, but I can provide some rationals.

    On heat pumps and simple hot gas defrost systems, they are there to provide a safety tank for unevaporated refrigerant that has been switched to travel back down the suction line from the evaporator.

    With low temperature refrigeration systems, iced up coils occur often enough to permit the exansion valves to overfeed and flood back to the compressors.

    Accumulators are not without their drawbacks. They are often made of steel and will rust through. They can plug the oil return oririfice and starve the compressor of oil. And finally... just how large should the accumulator be?

    I agree completely. Although, a good service tech should purge with N2 while braising so there should be nothing in the system to block the oil return orifice.

    Unless there has been a burnout where the burnout dryer should be place prior to the suction accumulator. As for "rusting"? If it is installed in a location where the system is prone to corosion I'd sujest giving it a coat of Kirby coat or Kill rust to be ultra safe. Will only cost you 50cents for that piece of mind. You would usually find a CPR valve after the accum. where there is H/G defrost. Applications with H/G defost in my opinion MUST have an accumulator.


  11. #11
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: accumulator

    Applications with H/G defost in my opinion MUST have an accumulator.
    Exactly the same statement that I made a short time age in a thread started by LC_shi regarding a de-humidifier project.

    Our friend M.O'b queried this stating that it was not necessary.

    Any comments anyone??

  12. #12
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: accumulator

    My experience with TXV's and refrigeration systems is one where I suggest an accumulator on any system. Sooner or later the system will exhibit some behavior where someone will wish they had installed one before the compressor went to pieces.

    It is simply cheap insurance for a lot of problems that can and do occur. Of course for some, the problem is simply being cheap and saving the upfront cost of the accumulator.

    Indeed, for hot gas systems the potential for liquid flood back is much higher and I would agree with the previous statement.

  13. #13
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: accumulator

    Quote Originally Posted by frank
    Exactly the same statement that I made a short time age in a thread started by LC_shi regarding a de-humidifier project.

    Our friend M.O'b queried this stating that it was not necessary.

    Any comments anyone??
    Needs an accumulator, or a re-evaporation coil. As per the thermostore set uo Iceman posted previous.

    Me I use an accumulator

    Kind Regards, Andy
    If you can't fix it leave it that no one else will:rolleyes:

  14. #14
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: accumulator

    HI Andy,

    Those Thermobank units were some of the first ones I found that were built without accumulators. And as usual they should have been supplied by the factory.

    Later versions are provided.

    Did not make for a very happy customer I can tell you.

Similar Threads

  1. DX v/s Gravity
    By Hemant Anand in forum Industrial
    Replies: 7
    Last Post: 19-07-2006, 02:16 AM
  2. Bearing trouble - rotary compressor
    By rosetennis in forum Industrial Compressors
    Replies: 6
    Last Post: 18-05-2006, 01:26 AM
  3. suction accumulator selection
    By Lc_shi in forum Fundamentals
    Replies: 9
    Last Post: 26-04-2006, 02:29 PM
  4. Frost on the suction line
    By lana in forum Trouble Shooting
    Replies: 19
    Last Post: 22-01-2006, 06:04 AM
  5. Suction Line Accumulator
    By bersaga in forum Commercial
    Replies: 11
    Last Post: 26-05-2003, 10:48 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •