    Freezer Problem



    Just looking for opinions on problems with a 2 door commercial freezer with temps in Celsius.
    Temperature 0° and rising.

    Suction line P/T at service port 5.7bar/3°
    Suction line at evap outlet 4°
    Compressor discharge pipe 2 inch from pot 126°
    Liquid line at condenser outlet 33°
    Condenser inlet 83°
    Air on condenser 29°
    Air off condenser 36°.
    Compressor amperage - 7amps.

    There's no service port to get high side gauge reading.



  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Freezer Problem

    Is it 404a Paul? if so compressor is goosed,if customer will pay then reclaim gas and try a fresh charge but i reckon compressor needs to come out
    Mostly found in the southern part of this green and pleasant land.

  3. #3
    Join Date
    Jan 2012
    Location
    Ireland
    Age
    39
    Posts
    18
    Rep Power
    0

    Re: Freezer Problem

    Quote Originally Posted by al View Post
    Is it 404a Paul? if so compressor is goosed,if customer will pay then reclaim gas and try a fresh charge but i reckon compressor needs to come out
    Yep...it's r404a! I think I'll go with the compressor so.

    Thanks!

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Freezer Problem

    Sometimes, R-404 is failing to perform and act just like you describe.
    just to be sure, reclaim the refrigerant and recharge to be sure its the compressor.
    Sound like a small unit with a small charge.

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Freezer Problem

    there is only 0.0'C suction super heat, suggest coil is flooding lifting SST and lack of performance. Discharge temp 126' c and condenser inlet 86' C.

  6. #6
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Freezer Problem

    Maybe there is an underlying fault should the compressor be....as AL says, Goosed.
    Check the defrost heater(s) aren't active while freezer is running it's cooling cycle.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  7. #7
    Join Date
    Mar 2009
    Location
    Uk
    Age
    41
    Posts
    121
    Rep Power
    17

    Re: Freezer Problem

    As Magoo has said you have 0K super heat. Are all the evaporator fans running? Is the evaporator coil clean? Also you say the discharge is 126 degrees but the inlet to the Condenser is 83 degrees. Does the discharge pipe go through a water collection tank? If so has it water in it as the discharge pipe is loosing a lot of heat before the condenser coil.

    Air on to the Condenser is 29 degrees and air off is 36 degrees. Is the Condenser coil clean. I would expect the TD to be higher unless the compressor is not pumping correctly. But if the compressor was not pumping correctly I would expect lower running amps.