    Window Unit AC modification into Split System? Possible? Help.



    I read this original thread some some ago and decided to give it a try.
    http://www.refrigeration-engineer.co...ystem-Possible
    Only performed the split idea and not the heat pump.
    Having a bit of trouble on the pressures though. Getting high suction and low liquid readings. Given enough running time the pressures will all but balance out. Thinking that the lack of a metering device has caused this. I thought that there might have been one in the evaporator. The origional suction line was 3/8 and has not been changed except for the additional 6 feet on line. On the liquid side the original line was something like 1/8 this was removed and was changed to 1/4, again with the additional 6 feet of line. On the origional setup there was no presence of a metering device. Not sure if the small liquid line assumed this roll. Not sure now how to install a piston and calculate this piston size. I could re- insert the 1/8 origional line before the evap and maybe this would work but I have decided for some advice before proceeding with any other possibilities.
    THANKS! !



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Window Unit AC modification into Split System? Possible? Help.

    Yes you cut out the 1/8 capillary metering line so the system will not work.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jul 2016
    Location
    usa
    Posts
    5
    Rep Power
    0

    Re: Window Unit AC modification into Split System? Possible? Help.

    Looks like the removed section of liquid line was actually a capillary metering device. Which is something I had not encountered before.

  4. #4
    Join Date
    Jul 2016
    Location
    usa
    Posts
    5
    Rep Power
    0

    Re: Window Unit AC modification into Split System? Possible? Help.

    What options are avaliable to the project now. Do txv valves come small enough? What about a piston?

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Window Unit AC modification into Split System? Possible? Help.

    I suppose you have discarded the original tubing.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Jul 2016
    Location
    usa
    Posts
    5
    Rep Power
    0

    Re: Window Unit AC modification into Split System? Possible? Help.

    I still have it however even withe the most amount of care the tube was crushed with the cutter. Also not sure how much line extends into the temporary fill port used by the manufacturer.

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Window Unit AC modification into Split System? Possible? Help.

    You normally cut capillary tubing by simply scoring a groove around the tube with a sharp blade and then snap it apart.

    You should be able to get replacement tubing from an HVACR supplier.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Jul 2016
    Location
    usa
    Posts
    5
    Rep Power
    0

    Re: Window Unit AC modification into Split System? Possible? Help.

    If the line would be about 1.5 inches shorter than originally. Would this cause problems?

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Window Unit AC modification into Split System? Possible? Help.

    Maybe but hopegully not too much.

    Put it in and see how it goes.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  10. #10
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,645
    Rep Power
    23

    Re: Window Unit AC modification into Split System? Possible? Help.

    If the system is 12,000 btu/h you can easily get a TXV for R-22 you need a txv with a VGA or VPC100 power head (This is the air con temp range, the 100 is the max operation pressure the valve will allow during hot pul down.)

    I been building a custom air handler for a similar project, only my system is 17.5K BTU/H I landed on the V-SBQ-A-VGA TXV from sporlan (V = R-22, SBQ-E is a OD sweat on type with external equalizer, A is the orifice size and will do 1.6 ton at 40F evap temp)

    For you I'd go with external equalize sweat on, but you won't need balanced port so:
    EBF - 2 - V - VGA - 1/4" x 3/8" x 1/4" Now that's for a sporlan valve, air conditioning at 1ton (12,000BTU/H)

    Selected with sporlan bulletins 10-9 / 10-10 and for the balanced port valves 10-10-6

    Or buy more 1/8 tubing and make a new cap tube metering device. Since you gon this far you may as well play with head control via fan cycling switch n so on
    Now in Redvers Sask.