    Question Liquid receiver volume .vs coils/heat exchangers volume



    Hello guys,

    I with my colleagues are working in air conditioning sector and step by step we are developing refrigeration systems. Refrigeration is quite new thing for us, so we don't know all the information (factors) that could affect performance of the system. We have made refrigeration system that we are testing in our climate chamber. So shortly about application:

    we are using finned air cooled coils (evaporator and condenser), variable speed compressor, eletronic expansion valve and other stuff (like suction accumulator, liquid receiver, filter drier and so on). Our application is reversible, so that means it's able to heat and cool.

    coils specification:
    - R410A refrigerant
    - in summer evaporator capacity 15,3 kw (at 8 C evaporating temperature)
    - evaporator inside volume - 8 litres
    - in summer condenser capacity 18,9 kw (at 47 condensing temperature)
    - condenser inside volume - 15 litres
    in winter system is reversed so evaporator works as condenser and condenser contrary (as evaporator).
    - in winter evaporator capacity 5,9 kw (at -14 C evaporating temperature)
    - evaporator inside volume - 15 litres
    - in winter condenser capacity 7,4 kw (at 27 C condensing temperature)
    - condenser inside volume - 8 litres

    system specification:
    - short piping system
    - liquid receiver volume - 2 litres

    I've made some refrigerant charge calculation according to defra calculator and it says that:
    - in summer maximum refrigerant charge approx 10,7 kg and minimum approx 7,1 kg
    - in winter maximum refrigerant charge approx 5,9 kg and minimum approx 4,4 kg

    Now our system is charged about 8 kg of refrigerant.

    The problem is that my colleagues say that system is overdesigned (coils inside volume differs almost 2 times). Also, when we're doing defrost in winter conditions (system is cooling, because evaporator is iced) we're almost working on low pressure limit (with the intense of low system charge).

    My questions:
    - What do you guys think, if we will add larger receiver (approx 7 litres, because coils inside volume differs of such amount), will our system work more properly?
    - If changing liquid receiver won't help, maybe there's only opportunity to reselect new coil that volume would be closer to 8 litres (instead of 15 litres)? What do you think?


    If you need any additional information, please write and I'll try to provide it.



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Liquid receiver volume .vs coils/heat exchangers volume

    Hi, Short answer remove liquid receiver in increase size of out door coil volume and surface area for pump down situations, a larger out door coil in cooling mode will increase sub cooling and efficiency, in heating mode will add surface area for heat recovery and reduce de ice cycles requirements.

  3. #3
    Join Date
    Feb 2015
    Location
    Lithuania
    Age
    33
    Posts
    20
    Rep Power
    0

    Re: Liquid receiver volume .vs coils/heat exchangers volume

    As I understand if I will remove receiver my system will suffer, because on different conditions (heating/cooling) I need different refrigerant charge (so receiver has to accumulate it). Removing receiver, will cause refrigerant conglomeration in condenser.

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Liquid receiver volume .vs coils/heat exchangers volume

    Sounds like you need a charge compensator such as this if i have understood your problem correctly,

    http://www.emersonclimate.com/Docume...ompensator.pdf
    Mostly found in Oxfordshire, UK :)

  5. #5
    Join Date
    Feb 2015
    Location
    Lithuania
    Age
    33
    Posts
    20
    Rep Power
    0

    Re: Liquid receiver volume .vs coils/heat exchangers volume

    I've read about that charge compensator and for other guys discussion I've realised that it's actually the same as liquid receiver.

    What do you guys think, if we will add larger receiver (approx 7 litres, because coils inside volume differs of such amount), will our system work more properly?

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Liquid receiver volume .vs coils/heat exchangers volume

    A charge compensator is not the same a a receiver. Basically depending on reversing valve mode either suction gas or discharge gas is piped through a tube in the center of it so either heating up or cooling down the body of the compensator. The compensator body is piped to the liquid line so when its cooled by suction gas the liquid refrigerant will condense in the body of it, and when its heated by discharge gas the liquid will be driven out. So totally unlike a receiver in operation. There is only one liquid connection so no flow through the device of liquid.
    Mostly found in Oxfordshire, UK :)

  7. #7
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: Liquid receiver volume .vs coils/heat exchangers volume

    Charge compensator accelerates the transition from AC to Heat Pump or vice versa and also shifts the charge from the low pressure duty (htg...) to the high pressure (cooling...). You have already identified the extent of charge shift, and your 2-litre HPR tolerates a swing charge certainly less than 2.2-Kg because as stored (heating) the HP liquid temp is about 27 C and its specific gravity about 1.08. That would appear to be substantially less than the charge swing so if you stick with an HPR it needs to be larger.