    problem with EXV on Daikin UATYQ



    Hi everyone.
    We have a problem with Daikin UATYQ600 rooftop unit.
    Each 20-30 minutes we have “high discharge temperature alarm” on 1st circuit. We check all sensors, EXV motors on each circuit, replace main and EXV PCB’s – nothing help.

    During the commissioning I found some strange behavior of EXV's. Without any explanation of their logic, I really cannot understand how they control suction superheat.
    EXV1 always tends to open, EXV2 – to close.
    I try to make a log file, but not all parameters in it. Please find it in attachment.
    UATYQ.zip

    Just after startup and during first 10-15 minutes of operation everything seems to be normal.
    But when some time is passing, EXV on first circuit start to open, IND HEX 1 temperature drops down.
    After couple of minutes this temperature stars to rise, and discharge temperature is rising also.

    Rooftop working conditions: outdoor ambient temperature 30-35C, suction air temperature doesn’t fall below 24-25C. Supply temperature about 18-17C.

    This unit is completely new, and was put in operation just two months ago.
    Also, we check refrigerant charge – it is according to specs for this unit – 10.4 kilo per circuit.

    Maybe somebody have an explanation of EXV logic? I cant find it on extranet, FQS doesnt provide any answer.
    Thank you in advance for your help.



  2. #2
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: problem with EXV on Daikin UATYQ

    Sh, sc, dsh

  3. #3
    Join Date
    Feb 2013
    Location
    Ukraine
    Age
    41
    Posts
    17
    Rep Power
    0

    Re: problem with EXV on Daikin UATYQ

    Solved. Wrong wiring from the factory.

  4. #4
    Join Date
    Aug 2009
    Location
    Dartford
    Age
    34
    Posts
    88
    Rep Power
    15

    Re: problem with EXV on Daikin UATYQ

    What was wired wrong

  5. #5
    Join Date
    Feb 2013
    Location
    Ukraine
    Age
    41
    Posts
    17
    Rep Power
    0

    Re: problem with EXV on Daikin UATYQ

    Quote Originally Posted by Deano240 View Post
    What was wired wrong
    EXV PCB. They was reversed.

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: problem with EXV on Daikin UATYQ

    Add voltage surge protection saves cooking PCBs