    Maneurop MTZ 100 internal relief problem on heat reclaim



    Hi All,
    Been a member of this forum for a long time now, enjoying everyone sharing their knowledge, this is my first post and would appreciate some feedback from around the globe.

    I've been working on a milk vat run by 2 maneurop mtz100's that has recently had a heat reclaim hot water system added into it. We were called out due to a slow pull down time and found the compressor to be venting on the internal relief valve. (Set at 30bar) R438a which equates to approx 70c) the hot water system is supposed to be set for 85c with electric booster elements of course)

    I guess my questions are

    Should there be a check valve installed in the discharge line to prevent higher pressures coming back to the compressor when the electric booster elements kick in?

    Could this high pressure coming back onto the head of the compressor caused the failure of the relief valve?

    Thanks for your time, hopefully you guys can give me some good feedback.

    Cheers



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Maneurop MTZ 100 internal relief problem on heat reclaim

    I guess something went wrong when the heat reclaim was installed.

    You should not heat the same water to 85C. It is much too high for the discharge temp.

  3. #3
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: Maneurop MTZ 100 internal relief problem on heat reclaim

    Is the discharge just piped through the heat exchanger with no valves or are there valves bypasses etc. A lot of these systems use a pressure regulator to keep the pressure high in the exchanger ,this is often to the detriment of the overall system . You really need a pressure reading before and after the exchanger before you go any farther

  4. #4
    Join Date
    Oct 2005
    Location
    australia
    Posts
    3
    Rep Power
    0

    Re: Maneurop MTZ 100 internal relief problem on heat reclaim

    Thanks joe-ice,
    The discharge is piped directly to the exchanger, no valves or bypasses. The only extra bit of gear on the discharge side is an oil seperator.
    I didn't design or install either the heat reclaim or any of the system, just one of the lucky ones that gets to fix it I guess.
    Have changed out the compressor but would like try and work out why it failed.

  5. #5
    Join Date
    Sep 2001
    Location
    London
    Age
    76
    Posts
    19
    Rep Power
    0

    Re: Maneurop MTZ 100 internal relief problem on heat reclaim

    The internal relief valve opens at 30 bar above crankcase pressure and will fully re-seat below 8 bar diff
    Should the valve open the gas will hit the internal Klixon and cause it to trip and under these circumstances could take about 2 hours to reset.
    Len Fiddler

  6. #6
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Maneurop MTZ 100 internal relief problem on heat reclaim

    Hi brassmonkey
    Can you make a sketch of the components in the discharge line with the heat recovery unit. The HR once up to temperature should bypass the gas to the normal ambient condenser. The condenser and HR can be piped in series or parallel but needs proper discharge temperature control to prevent cooking the compressor. Show us whats on the system and we can try to advise