    Sep 2014
    Australia
    9
    Liquid line drier sizing
    I'm working on a Temerzone BD1250R (125kw).
    Stages - 4
    Refrigerant 4 x 7.26kg R407C
    Compressor run amps - 4 x 14.9
    Currently each stage has 2 x 084S driers in parallel. I would like to know if I can change these out with one larger drier (they are in an awkward position to change). I also service other Package units that have no driers straight out of the factory! So I am after some good information on how to size a liquid line drier.
    Cheers guys.
    Sep 2014
    Australia
    9
    Re: Liquid line drier sizing
    As an addition to the post above I see that the Actrol catalogue lists their drier by Liquid flow capacity:kw. Does anyone know if this correlates to system capacity. If not what is liquid flow capacity.
    Some examples out of their catalogue:
    BFK084S 1/2" Solder Liquid flow cap (kw) 134a=23.6, R22=23.6, R404a/R507=23.2
    BFK165 5/8" male flare Liquid flow cap (kw) 134a=30.6, R22=30.6, R404a/R507=29.9
    BFK305 5/8" male flare Liquid flow cap (kw) 134a=36, R22=36, R404a/R507=35.4
    BFK307S 7/8" Solder Liquid flow cap (kw) 134a=58.7, R22=58.7, R404a/R507=57.7
    Sep 2003
    ISRAEL
    66
    4,171
    40
    Jan 2007
    India
    13
    Yes , the liquid capacity relates your system capacity with respect to 1 psig pressure drop at rated condition . you can match your system capacity at the rating condition and choose the filter drier accordingly.
    As chemi suggested you can use the replaceable core type filter drier . You can also use the product selection software of Danfoss for their drier selection http://refrigerationandairconditioni.../coolselector/