    System vacuum



    Hello,

    I have one question, is there something wrong to vacuum the system below 200 microns if there is oil filled compressor? Couldn't I we damage the oil?



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: System vacuum

    No, actually, any refrigerant left in the oil will boil out. It does good to the oil.

  3. #3
    Join Date
    Jun 2016
    Location
    Lithuania
    Posts
    5
    Rep Power
    0

    Re: System vacuum

    Quote Originally Posted by chemi-cool View Post
    No, actually, any refrigerant left in the oil will boil out. It does good to the oil.
    But if we vacuum our new system before the refrigerant filling?

  4. #4
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: System vacuum

    Pulling a vacuum on the system removes both air and moisture . Oil as new in a system will contain some moisture especially POE oil and during the dehydration process this moisture will be removed from the system prior to the refrigerant being charged. So unless the oil is dehydrated along with the complete system then the system moisture content may be above safe limits for the plant and possible lubrication failure may occur causing the compressor to fail or other system components which could prevent the plant functioning correctly

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: System vacuum

    Also, if possible have yhe crankcase heater active when evacuating the system.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: System vacuum

    http://alltemp.ca/wp-content/uploads...Presention.pdf

    See page 33 indicates damage to oil at 200 microns or less due to oil vapour pressure.
    Says not to go below 500 microns.

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: System vacuum

    Quote Originally Posted by Glenn Moore View Post
    Oil as new in a system will contain some moisture especially POE oil and during the dehydration process this moisture will be removed from the system prior to the refrigerant being charged.
    Hi Glen! Are you sure that oil could be dehydrated by vacuum drying?
    What I fond here on forum, and elsewhere on internet, is opposite to that statement.
    Moisture from oil cannot be removed easily by vacuum drying. Moisture and oil has strong molecular bonds.
    Moisture in oil could be removed in chemical reaction with desiccant in filter dryer!
    That is sum of what I found on that subject.
    I think vacuum drying below 200 microns in order to remove moisture from oil is pointless.
    Last edited by nike123; 03-07-2016 at 08:10 PM.

  8. #8
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    867
    Rep Power
    26

    Re: System vacuum

    Seems to me I learned a long time ago that mineral oil boiled at about 200-250 microns.
    Always made me think I was being bull****ed when someone claimed that they pulled a system down to 75 microns. Which a major manufacturer told me they did.
    And there was oil in the compressor.
    Seems to me that too low a vacuum would redistill the oil into something I might not want.