    Jun 2016
    Egypt
    3
    Condensing Unit selection ?
    Can someone help me to select the right condensing unit that fulfills the following specification :
    Capacity=.8 KW (I think it's too low put my application to cool 5 litres of antifreeze to -20C)
    Evaporating temperature=-25C
    Condensing temperature=40C
    Superheat=10
    subcooling=10 these two are recommendations and can be changed if I am wrong?
    I am using coolpack to get the cycle information for R-22 and R404A
    The Refrigerant: R22
    Data:
    Te [C] = -25.00
    Tc [C] = 40.00
    DT subcooling [K] = 10.00
    DT superheat [K] = 10.00
    Isentropic efficiency = 1.00
    Calculated:
    Qe [kJ/kg] = 165.098
    Qc [kJ/kg] = 219.861
    W [kJ/kg] = 54.763
    COP [-] = 3.01
    Pressure ratio [-] = 7.630
    Refrigerant: R404A
    Data:
    Te [C] = -25.00
    Tc [C] = 40.00
    Calculated:
    Qe [kJ/kg] = 115.920
    Qc [kJ/kg] = 158.189
    W [kJ/kg] = 42.270
    COP [-] = 2.74
    Pressure ratio [-] = 7.266
    As you can see the cop for R-22 is higher and it's price is much less than R404A
    but when I go to http://www.embraco.com/catalog/Default.aspx?language=EN
    to select a condensing unit as they are available in my country if found the evaporating temperature for R22 is ranging from -15 to 10C ?
    Can someone please help me cause I am not an expert if something i don't understand please tell me.
    Sep 2003
    ISRAEL
    66
    4,119
    38
    Re: Condensing Unit selection ?
    I think this unit will be ok for your application - UC UNT2180GK 220V/50Hz 515301512
    I would use 507 as refrigerant, you can use also 22 with the same condensing unit.
    Jun 2016
    Egypt
    3
    Thank you for your answer I really appreciate.
    In the product specification, the refrigerant is 404A is that alright? Can I use another refrigerant while the specification recommends a specified one?
    One more think if you excuse me
    do you use the website (http://www.embraco.com/catalog/Default.aspx?language=EN) for selection or you go to pdfs catalog?
    Sep 2003
    ISRAEL
    66
    4,119
    38
    You can use 404, 507 or 22. Just make sure that oil is POE. With 22 you will get lower discharge pressure.
    I use my supplier web page for selection.
    Good luck with your project.