Hi guys need your help.
I have Carrier unit "oasis 250" model
My problem is "the unit when it running in diesel mode and it just continue running?/working/
Setting is "3 degrees" and in cycle mode "on"
most of the time before it reach 3 degrees the unit will stop/cutoff but then immediately it will start/cut-in again while in 3 degrees, i try also to to make "cycle mode off" but still same problem 3 degrees off but at the same time it will running again.
i check it also in electric mode it stop at 3 degrees and start at 6 degrees which is o.k normal
i have check & replace all my sensor, pc board, microprocessor, cab control
but still the same problem again
-
28-06-2016, 05:42 PM #2
Re: Carrier Transicold Oasis 250
Check your water temperature sensor. The unit will not cycle off if water temp is below 50C. A restart is forced if water temp drops below 1C. Also battery voltage, it will not cycle off until battery is 13.4 VDC. A + sign should appear beside the voltage reading when battery voltage is satisfied. Water temp is ignored in standby.
-
01-07-2016, 08:08 PM #3
Re: Carrier Transicold Oasis 250
Sir IRMechanik,
Thanks for the information it helps me a lot.