Thread: ac unit condensate water
27-06-2016, 05:26 PM #1
Hi all
i have question about water condensates from ac unit which drained outside
if AC unit works perfectly
then y sometimes there will be no water drain
or why it will be too much water
what condition that could prevent it or decrease or increase itPower consists not in being able to strike another but in being able to control oneself when anger arises
27-06-2016, 08:31 PM #2
Re: ac unit condensate water
It depends on the ambient humidity level whether there is any excess moisture to be removed from the air.
27-06-2016, 08:51 PM #3
outdoor humidity is 19%
temperature is 46 CPower consists not in being able to strike another but in being able to control oneself when anger arises
27-06-2016, 09:49 PM #4
When it comes to AC and humidity it is the room humidity that counts.
But with ambient being as low as 19% I guess the room humidity would be really low as well.
Generally if you have a room humidity of less than ~30% there will be little or no dehumidification by the evaporator and therefore little or no condensate.
If on the other hand you got a high room humidity there will be vast amounts of condensate.
27-06-2016, 10:22 PM #5
Hi Kefah,
Glad to see you are keeping well.
Stay safe,