Results 1 to 4 of 4
Thread: Condensor capacity
Hybrid View
27-06-2016, 02:04 PM #1
Condensor capacity
Hi,
I am sizing a condensor unit based on capacity. Can someone confirm my capacity calculation.
1. I start with an evaporator capacity of 160kW. With the refrigerant enthalpies and capacity of 160kW I calculate the massflow. Massflow=Capacity_evap / (Enthalpy_out - Enthalpy_in) Units of enthalpy are in kJ/kg
2. With the massflow calculated in step 1 and the working conditions of the condensor I determine the enthalpies in the condensor. The condensor capacity is then Capacity_cond = Massflow x (Enthalpy_cond_in - Enthalpy_cond_out)
Is this the right method of determining the required condensor capacity?
Please let me know many thanks in advance
27-06-2016, 02:53 PM #2
Re: Condensor capacity
evaporator capacity at designed temp + compressor watt draw + 15% for a warm day.
Thats the way I do it.
28-06-2016, 09:57 AM #3
I agree with Chemi cool .I consider Evaporator capacity + compressor Power consumption + 10% for losses
29-06-2016, 04:58 AM #4
I have never been a fan of "Rule of Thumb" calculations, especially if evap loading is 160kws.
generally use a long and protracted method, especially if located in the Nederlands. Ambient conditions are so varied, summer to winter