    Jun 2016
    the Netherlands
    2
    Condensor capacity
    I am sizing a condensor unit based on capacity. Can someone confirm my capacity calculation.
    1. I start with an evaporator capacity of 160kW. With the refrigerant enthalpies and capacity of 160kW I calculate the massflow. Massflow=Capacity_evap / (Enthalpy_out - Enthalpy_in) Units of enthalpy are in kJ/kg
    2. With the massflow calculated in step 1 and the working conditions of the condensor I determine the enthalpies in the condensor. The condensor capacity is then Capacity_cond = Massflow x (Enthalpy_cond_in - Enthalpy_cond_out)
    Is this the right method of determining the required condensor capacity?
    Please let me know many thanks in advance
    Sep 2003
    ISRAEL
    65
    4,116
    38
    Re: Condensor capacity
    evaporator capacity at designed temp + compressor watt draw + 15% for a warm day.
    Thats the way I do it.
    Jan 2007
    India
    61
    13
    I agree with Chemi cool .I consider Evaporator capacity + compressor Power consumption + 10% for losses
    Auckland
    67
    3,362
    31
    I have never been a fan of "Rule of Thumb" calculations, especially if evap loading is 160kws.
    generally use a long and protracted method, especially if located in the Nederlands. Ambient conditions are so varied, summer to winter