25-06-2016, 08:34 AM #1
Re: R134a Low Subcooling, High Superheat
The cooler cuts off as the water cooler is designed to make sure that water temperature doesn't drop below 7 deg. C. The users don't prefer water colder than that.
Last edited by yash7; 25-06-2016 at 08:50 AM.
-
25-06-2016, 12:52 PM #2
Re: R134a Low Subcooling, High Superheat
-
26-06-2016, 04:27 PM #3
Re: R134a Low Subcooling, High Superheat
The problem is actually the COP. It is very less. The compressor is consuming about 100 W and the rate of cooling is very slow. The average cooling capacity is about 62 W and it took nearly 25 mins to pull down the temperature from 35 to 7 degrees C (0.8L water). As per the compressors' datasheet, for 54.4 deg. C condenser temperature, and -10 degrees C evaporator temperature, the power consumption is 100 W and the capacity is 135W. I had expected that at nearly the same condenser temperature, and higher evaporator temperature, the capacity should be even higher and that low/no subcooling, and the subsequent reduction in flow rate by the throttling device are lowering the capacity. Where am I going wrong?
Last edited by yash7; 26-06-2016 at 04:38 PM.