09-06-2016, 09:18 AM #1
thermoking/MD200
hello everybody.my name is Nelson,i have problem in Thermoking MD200.the low pressure is 20psi & high pressure is 350psi (R404a) but the box Temp.is only 15*c ..can you give me an idea what is totally problem..temperature must be -18*c...thank you guys.
-
20-06-2016, 08:09 PM #2
Re: thermoking/MD200
how big is the box ? Have you tried it with a at temp load ?
-18 from a MD200 in high ambient could be a big ask
The pressures sound normal for your ambient
-
21-06-2016, 01:18 AM #3
Re: thermoking/MD200
20 psi suction is the CPR setting.
What is the temperature difference?
Is the three way sealing?
Is it flooding?
Is the ball up?
Is the condenser clean?