    Question Carrier Transicold Oasis 250



    Hi guys need your help.
    I have Carrier unit "oasis 250" model
    My problem is "the unit when it running in diesel mode and it just continue running?/working/

    Setting is "3 degrees" and in cycle mode "on"

    most of the time before it reach 3 degrees the unit will stop/cutoff but then immediately it will start/cut-in again while in 3 degrees, i try also to to make "cycle mode off" but still same problem 3 degrees off but at the same time it will running again.

    i check it also in electric mode it stop at 3 degrees and start at 6 degrees which is o.k normal

    i have check & replace all my sensor, pc board, microprocessor, cab control
    but still the same problem again



  2. #2
    Join Date
    Aug 2011
    Location
    Canada
    Posts
    160
    Rep Power
    15

    Re: Carrier Transicold Oasis 250

    Check your water temperature sensor. The unit will not cycle off if water temp is below 50C. A restart is forced if water temp drops below 1C. Also battery voltage, it will not cycle off until battery is 13.4 VDC. A + sign should appear beside the voltage reading when battery voltage is satisfied. Water temp is ignored in standby.

  3. #3
    Join Date
    Jun 2016
    Location
    Saudi Arabia
    Posts
    2
    Rep Power
    0

    Re: Carrier Transicold Oasis 250

    Sir IRMechanik,

    Thanks for the information it helps me a lot.