Results 1 to 9 of 9
Thread: r 22
    Nov 2012
    EYGPT.DAMITTA
    37
    r 22
    hi all
    how about r22
    in jordan
    replace r404 a to r22 its so fast
    I have some problems with ***** R-404 A
    I am doing my change-dried filter every 6 months
    Clean condenser and evaporator always
    Check the compressor and use the original oilsCooling is always very slow does not decline more than -5 C
    Ambient temperature in the Middle East, rising to 50 degrees Celsius
    May 2011
    Romania
    35
    83
    8
    Re: r 22
    original 404a systems have bigger condensers and almost always subcool liquid, r22 systems don't. also r22 systems usually have liquid injection to cool compressor, remove this if you change to 404... it will never work the same with 404....
    Aug 2011
    Canada
    160
    9
    Re: r 22
    Running R-22 without a quench valve (liquid injection) is asking for trouble.
    In 30 degree ambient an R-22 system will be quenching, in 50 degree ambient without a quench valve you're going to burn the compressor down.
    I would think the expansion valve would need to be changed as well.
    Feb 2009
    telford
    2,068
    27
    Re: r 22
    Big mistake to change to r22,if your ambient is that high then getting your trailers in the shade then precooling is the answer ,if you do not fit liquid injection to an r22 system the compressor is going to go bang!
    Nov 2012
    EYGPT.DAMITTA
    37
    Re: r 22
    So how do you raise the cooling performance with R-404
    Feb 2009
    telford
    2,068
    27
    Re: r 22
    In that ambient your box /trailer need to be in very good condition have you cleaned the evaporator I would look at putting liquid nitrogen blast into the box to help the cooling process
    Feb 2009
    telford
    2,068
    27
    Re: r 22
    What model of unit is fitted to the trailer?
    Nov 2012
    EYGPT.DAMITTA
    37
    Re: r 22
    All types of trailers
    Melbourne
    349
    12
    Re: r 22
    if your relying on the european range of fridges you might have problems.
    You might want to look at importing second hand SB310 or SB330 thermo king units, there good in the heat, and most parts are the same as Thermo Kings available in europe.