    R22 low subcooling



    r22 2 ton goodman no txv. outside air temp 90.31 deg. split temp air intake and best register.low side 67, high side 218. superheat 18 subcooling 1.3. tech came out said system has noncondensables. want to recover *****,clean evap coils and pull vacuum. recharge. r22 is very expensive, could he just pump down,clean coils, vacuum and recharge?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: R22 low subcooling

    It depends, what is the legal stance were you are with regards to using R22 as it is now a banned refrigerant.

    Other than that, if the refrigerant has non-condensibles then it can be cleaned but that costs money also.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jun 2016
    Location
    United States
    Posts
    4
    Rep Power
    0

    Re: R22 low subcooling

    still have here in texas. 450 dollars 30 lb bottle.

  4. #4
    Join Date
    Jun 2016
    Location
    United States
    Posts
    4
    Rep Power
    0

    Re: R22 low subcooling

    tech came. recovered my ***** to clean bottle.cleaned evap and cond coils. checked amps on fans. all good. vacuumed sytem. added ***** back. charged me for 1 lb. new numbers are inside wet bulb 60f. outside dry bulb 84. low press 70 high press 178. SH 1.6...SC 4.7... target SH 8.6 on feildpeice. he said im good and left. 625 dollars. hope it works. feedback please.

  5. #5
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: R22 low subcooling

    Quote Originally Posted by dwsmith43 View Post
    still have here in texas. 450 dollars 30 lb bottle.
    Multiply your $ 450 USD by 5 and convert to OZ $. R22 here is close to the phase out stage.
    Last edited by mikeref; 22-06-2016 at 09:02 AM. Reason: Currently one AU $ is 75 Cents Merican
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: R22 low subcooling

    Quote Originally Posted by dwsmith43 View Post
    tech came. recovered my ***** to clean bottle.cleaned evap and cond coils. checked amps on fans. all good. vacuumed sytem. added ***** back. charged me for 1 lb. new numbers are inside wet bulb 60f. outside dry bulb 84. low press 70 high press 178. SH 1.6...SC 4.7... target SH 8.6 on feildpeice. he said im good and left. 625 dollars. hope it works. feedback please.
    According to these numbers, the SCT is 10F over outdoor ambient with low superheat. Maybe I'm wrong or maybe the numbers are wrong, but this doesn't look good.

  7. #7
    Join Date
    Jun 2016
    Location
    United States
    Posts
    4
    Rep Power
    0

    Re: R22 low subcooling

    your right about that. 86 degrees in the house. 88 outside. on the upside, less humidity in here.

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: R22 low subcooling

    I would remove refrigerant very slowly until the superheat is at least 10F... and hope the valves are not broken.