    R410A outdoor using R22 indoor (non inverter split)



    Hi. Is it possible to replace a R22 FCU to a R410A outdoor?



  2. #2
    Join Date
    Oct 2007
    Location
    sweden
    Posts
    93
    Rep Power
    20

    Re: R410A outdoor using R22 indoor (non inverter split)

    R22 have 14.3 Bar @ 40 degree C

    R410A have 23.3 Bar @ 40 degree C

    Equipment should be survive and not start to leak (and in worst case explode) even if whole, non running package heating up 40-50 degree C environment temperature.

    So short answer No!, you cannot use same indoor-unit for R22 to outdoor unit for R410A

    and even if you try, efficiency should not be good ie. indoor unit for R410A is different optimized (smaller pipes etc.) for higher density working refrigerant.

  3. #3
    Join Date
    Jun 2016
    Location
    Malaysia
    Posts
    9
    Rep Power
    0

    Re: R410A outdoor using R22 indoor (non inverter split)

    Quote Originally Posted by xxargs View Post
    R22 have 14.3 Bar @ 40 degree C

    R410A have 23.3 Bar @ 40 degree C

    Equipment should be survive and not start to leak (and in worst case explode) even if whole, non running package heating up 40-50 degree C environment temperature.

    So short answer No!, you cannot use same indoor-unit for R22 to outdoor unit for R410A

    and even if you try, efficiency should not be good ie. indoor unit for R410A is different optimized (smaller pipes etc.) for higher density working refrigerant.
    Thanks any chance if to retrofit it?

  4. #4
    Join Date
    Jun 2016
    Location
    Malaysia
    Posts
    9
    Rep Power
    0

    Re: R410A outdoor using R22 indoor (non inverter split)

    Quote Originally Posted by xxargs View Post
    R22 have 14.3 Bar @ 40 degree C

    R410A have 23.3 Bar @ 40 degree C

    Equipment should be survive and not start to leak (and in worst case explode) even if whole, non running package heating up 40-50 degree C environment temperature.

    So short answer No!, you cannot use same indoor-unit for R22 to outdoor unit for R410A

    and even if you try, efficiency should not be good ie. indoor unit for R410A is different optimized (smaller pipes etc.) for higher density working refrigerant.
    Thanks any chance if to retrofit it?

  5. #5
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: R410A outdoor using R22 indoor (non inverter split)

    Quote Originally Posted by hvac_weng View Post
    Thanks any chance if to retrofit it?
    no just don't.