    Danfoss CDS 303



    Is there anyone familiar with that speed controller?

    A few issues left to solve.

    Thaks.



  2. #2
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Danfoss CDS 303

    Hi Chemi
    What's the issue . If I can't help I'm still in contact with my Danfoss drives colleagues who can help Glenn

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Danfoss CDS 303

    The CDS is controlling VZH117 scroll.
    I get overcurrent massage when starts.
    Megger it - ok.
    Between phases - 0.6 Ω
    How do I check the current setup?
    Is it ok to connect it without the controller to the mains for a few seconds to see if it is ok?

  4. #4
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Danfoss CDS 303

    Check parameter 4-18 which should be Motor Overcurrent setting

    The CDS drive has an in built wizard with the compressor information settings pre set . The overcurrent setting is therefore also preset, so check that the correct compressor has been selected . Also check the motor details on the compressor as Maneurop often use 230 volt 3 phase motors with the drive to enhance the motor

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Danfoss CDS 303

    Thanks Glenn.
    I will be there monday morning and check all the compressor motor parameters.

    You will be informed of my finding.
    I have a feeling that when I changed the CDS to 0-10v, I might have changed also something else cause it was working fine before.

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Danfoss CDS 303

    Hi Glenn,
    checked it all and all parameters are ok.
    Checked compressor direct line, got 1320 Amps before current overload tripped.
    So, as for today, compressor needs to be replaced.
    Thanks for your help.

  7. #7
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Danfoss CDS 303

    Ok chemi
    Br Glenn