09-06-2016, 06:39 PM #1
Danfoss CDS 303
Is there anyone familiar with that speed controller?
A few issues left to solve.
Thaks.
-
09-06-2016, 07:00 PM #2
Re: Danfoss CDS 303
Hi Chemi
What's the issue . If I can't help I'm still in contact with my Danfoss drives colleagues who can help Glenn
-
09-06-2016, 07:50 PM #3
Re: Danfoss CDS 303
The CDS is controlling VZH117 scroll.
I get overcurrent massage when starts.
Megger it - ok.
Between phases - 0.6 Ω
How do I check the current setup?
Is it ok to connect it without the controller to the mains for a few seconds to see if it is ok?
-
10-06-2016, 11:15 AM #4
Re: Danfoss CDS 303
Check parameter 4-18 which should be Motor Overcurrent setting
The CDS drive has an in built wizard with the compressor information settings pre set . The overcurrent setting is therefore also preset, so check that the correct compressor has been selected . Also check the motor details on the compressor as Maneurop often use 230 volt 3 phase motors with the drive to enhance the motor
-
10-06-2016, 12:31 PM #5
Re: Danfoss CDS 303
Thanks Glenn.
I will be there monday morning and check all the compressor motor parameters.
You will be informed of my finding.
I have a feeling that when I changed the CDS to 0-10v, I might have changed also something else cause it was working fine before.
-
13-06-2016, 02:08 PM #6
Re: Danfoss CDS 303
Hi Glenn,
checked it all and all parameters are ok.
Checked compressor direct line, got 1320 Amps before current overload tripped.
So, as for today, compressor needs to be replaced.
Thanks for your help.
-
13-06-2016, 06:09 PM #7
Re: Danfoss CDS 303
Ok chemi
Br Glenn