    thermoking/MD200



    hello everybody.my name is Nelson,i have problem in Thermoking MD200.the low pressure is 20psi & high pressure is 350psi (R404a) but the box Temp.is only 15*c ..can you give me an idea what is totally problem..temperature must be -18*c...thank you guys.



  2. #2
    Join Date
    Dec 2007
    Location
    Melbourne
    Posts
    347
    Rep Power
    18

    Re: thermoking/MD200

    how big is the box ? Have you tried it with a at temp load ?
    -18 from a MD200 in high ambient could be a big ask
    The pressures sound normal for your ambient

  3. #3
    Join Date
    Aug 2011
    Location
    Canada
    Posts
    160
    Rep Power
    15

    Re: thermoking/MD200

    20 psi suction is the CPR setting.
    What is the temperature difference?
    Is the three way sealing?
    Is it flooding?
    Is the ball up?
    Is the condenser clean?