    Mitsi ae200 showing units in fault but no fault code



    I have recently changed an mj180 to an ae200 central controller.
    The ae200 has 2 ew50 expansion boards connected.
    Everything is working fine except their are about 10 units that are showing on the screen that they are in fault and arnt operating, however when you click the alarm log their are no faults for these units. When I open the outdoor unit covers they are ready to go and have no alarms up, can anyone shed some light on this.



  2. #2
    Join Date
    Feb 2011
    Location
    England
    Posts
    44
    Rep Power
    0

    Re: Mitsi ae200 showing units in fault but no fault code

    You might have to perform a Virgin restart to clear the faults.

  3. #3
    Join Date
    Jun 2016
    Location
    Northern Ireland
    Age
    29
    Posts
    3
    Rep Power
    0

    Re: Mitsi ae200 showing units in fault but no fault code

    I'm not that familiar with mitsi kit, can you explain how to do a virgin restart

  4. #4
    Join Date
    Mar 2009
    Location
    Uk
    Age
    41
    Posts
    121
    Rep Power
    17

    Re: Mitsi ae200 showing units in fault but no fault code

    When you go into log, you have communication error on one icon and unit error on the other. Are you sure you don't have any faults in the communication icon?

  5. #5
    Join Date
    Jun 2016
    Location
    Northern Ireland
    Age
    29
    Posts
    3
    Rep Power
    0

    Re: Mitsi ae200 showing units in fault but no fault code

    Turned out that the voltage in the mnet had dropped to 23volts dc from the ae200 to the outdoor units.
    Fitted a booster pack to bring the voltage to 30vdc and the units started working.
    For anyone that is wondering to do a virgin restart
    You power down outdoors- bc boxes and indoors
    Switch 2- switch on dip 3 and 2
    Power up the unit
    Wait until 1 is displayed on outdoor
    Power down and put dipswitches back to normal
    Wait 10 minutes power up indoor outdoor and bc boxes