    Lightbulb Scroll fan rattle problem FTKS71HVMG



    Dear All,

    I am new and an aspiring DIY enthusiast and i have been cleaning my own mini split a Daikin FTKS25DVM with no problems. Enough with my mini intro and with a proper description of my problem as below.

    My gf's FCU which is a FTKS71HVMG has been experiencing a scroll fan rattle and I have visual confirmation that it is a particular impeller rim that has been hitting the frame of the housing causing the rattle.

    In addition, i found that the hex socket screw (grub screw) that supposedly secures the scroll fan to the spindle was missing. I located a screw specialist and promptly bought a 4MX6 and secured it.

    It was a pain in the butt to secure that screw because i had no idea how to remove the drain tray which prevented easy access. On the smaller FTKS25DVM, i could access a screw in the inner recess behind (and in between) the electrical panel as well as the A tower coil. Some torsion twist and turns, the drain tray could be out. I am just stumped by the FTKS71HVMG.

    I thought the removal procedure would be the same but i think i am wrong.

    Can anyone comment on

    1.) What i can do to remove the drain tray
    2.) The cause of the scroll fan rim hitting the housing?

    Very much appreciated!



  2. #2
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    438
    Rep Power
    32

    Re: Scroll fan rattle problem FTKS71HVMG

    http://www.daikinac.com/content/asse...ice-Manual.pdf

    I would guess the fan motor bearings have worn.
    I love the smell of Ammonia in the morning!

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Scroll fan rattle problem FTKS71HVMG

    Quote Originally Posted by happily1986 View Post

    1.) What i can do to remove the drain tray
    2.) The cause of the scroll fan rim hitting the housing?

    Very much appreciated!
    1. Nothing. Drain tray is integral part of indor unit housing. Fan cage cannot be removed without removing first the heat exchanger.
    2. Loose fixing screw. It should be 5mm gap between fan cage and housing.