    Fujitsu nocria



    Indoor unit no power indication. Got live on neutral terminal and nothing on live terminal on indoor unit output to outdoor unit. When tested on outdoor unit before disconnecting, got 230v on live and neutral terminals. Diagnosed indoor pc board fried. Anyone had this before?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Fujitsu nocria

    230 on neutral terminal means that your neutral feed is broken.

    Check the mains supply.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2016
    Location
    New zealand
    Posts
    6
    Rep Power
    0

    Re: Fujitsu nocria

    I did check live to neutral 230v, live to earth 230v on incoming supply. Is there something else i should check on the incoming? I opened and checked Wiring at isolator also okay. Called fujitsu tech support, ran trough tests with them and problem still not solved. Tech tells me he had same problem on his unit, opened everything and when closed starts up fine. Not much help there. With the outdoor completely disconnected along with its earth, I find 230 on neutral, 0 on live terminal for outdoor connetion terminals on indoor unit. Even with the outdoor unit completely disconnected, will the indoor unit still be able to switch on as the supply runs traight to the indoor board? I also disconnected everything else from indoor unit with only the power supply connected and still nothing.