    compressor terminal blow up cause



    Hi all
    i got 12000 BTU R22 ac Split unit with shorted compressor]
    so i installed new one
    charged by weight

    it was cooling very good
    for one day
    after 1 day perfect work
    i got call its not cold and trip circuit breaker
    got there to find that compressor both C & R blown up
    with black residue around it
    what the cause behind 2 terminal blow up???


    Power consists not in being able to strike another but in being able to control oneself when anger arises

  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: compressor terminal blow up cause

    Whatever caused the first compressor to short has caused the second to fail. flush the system pipe work, maybe install a suction filter (if cooling only unit), run nitrogen through the lines and pressure test, then a good vacuum.
    Mostly found in the southern part of this green and pleasant land.

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: compressor terminal blow up cause

    common an run terminals scorched /blown- overcurrent from a seizing compressor?, did you replace the original electrics, capacitor, relay

  4. #4
    Join Date
    Jun 2014
    Location
    Scotland
    Age
    40
    Posts
    38
    Rep Power
    0

    Re: compressor terminal blow up cause

    Sounds like you could have acid in the system.

  5. #5
    Join Date
    Feb 2015
    Location
    India
    Posts
    43
    Rep Power
    0

    Re: compressor terminal blow up cause

    @kefah, with 599 post as of today you sure are expert!
    System, sure, must be having solid particles which have damaged the compressor motor windings thus leading to heavy short circuit current flowing through the terminals and eventually burning them. Before your next venture with new compressor, blow thoroughly the entire system with nitrogen, make sure system is clean of any solid particles. Install a filter cum dryer prior compressor, before releasing gas into the new compressor + system, good vacuum is essential.
    Can brazing be avoided? Instead Use brass compression unions if possible.
    I maintain, everything I have, myself.

  6. #6
    Join Date
    Feb 2015
    Location
    India
    Posts
    43
    Rep Power
    0

    Re: compressor terminal blow up cause

    Posted twice, regrets!
    Last edited by vikky1971; 30-05-2016 at 10:47 PM. Reason: Posted twice
    I maintain, everything I have, myself.

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: compressor terminal blow up cause

    Good to hear from you Kefah, hoping you are still safe.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: compressor terminal blow up cause

    kefah
    when changing a burnt out compressor it is important to protect the new compressor from the burn out contaminants in the system. Most modern day compressors have in built safety components such as Klixons or thermistors which normally prevent the total destruction of the motor windings. But in any hermetic or semi hermetic system the combination of oil, refrigerant, heat electrical arcing in the motor etc will cause weak acids to manifest themselves in the oil and refrigerant and these acids start to attack the motor insulation (shilac) and bare electrical parts inside the machine. Poor evacuation of a system will make the situation worse.
    So when fitting a replacement compressor it is necessary to fit a BURN OUT Drier to the suction line close to the compressor, and ideally a standard drier in the liquid line exiting the condenser.
    The Burn Out Drier core is made from pure Activated Oxides which will remove any acid products from the suction gas and oil returning to the compressor, thereby protecting the new compressor, the drier in the liquid line has a combination core made up from silica gel, molecular sieve, and a small percentage of activated Oxides, this drier will remove any moisture in the system and also some of the acids.
    After a few days these driers can be replaced with new ones and after that they can be totally removed from the system, as you remove the acidic contaminants with the used driers.
    It sounds that the system is badly contaminated so to prevent more burn outs make sure a good quality BURN OUT drier is fitted to protect the compressor. Many engineers make the mistake of changing the compressor and sometimes the liquid line drier but fail to fit the most important one the BURN OUT drier. All the manufacturers manufacture them

  9. #9
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: compressor terminal blow up cause

    Quote Originally Posted by install monkey View Post
    common an run terminals scorched /blown- overcurrent from a seizing compressor?, did you replace the original electrics, capacitor, relay
    i replaced only wires
    Power consists not in being able to strike another but in being able to control oneself when anger arises

  10. #10
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: compressor terminal blow up cause

    Quote Originally Posted by Craig Johnston View Post
    Sounds like you could have acid in the system.
    i didnt flush the system
    Power consists not in being able to strike another but in being able to control oneself when anger arises

  11. #11
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: compressor terminal blow up cause

    ok thank u all for important advice
    my question could acid damage compressor after 1 day???

    as i think it could take longer time
    Power consists not in being able to strike another but in being able to control oneself when anger arises

  12. #12
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: compressor terminal blow up cause

    Quote Originally Posted by vikky1971 View Post
    @kefah, with 599 post as of today you sure are expert!
    System, sure, must be having solid particles which have damaged the compressor motor windings thus leading to heavy short circuit current flowing through the terminals and eventually burning them. Before your next venture with new compressor, blow thoroughly the entire system with nitrogen, make sure system is clean of any solid particles. Install a filter cum dryer prior compressor, before releasing gas into the new compressor + system, good vacuum is essential.
    Can brazing be avoided? Instead Use brass compression unions if possible.
    for dryer filter u talk u correct
    i will be more careful next time