    Suction temperature too high alarm of trane cgam chiller



    I have an alarm in our chiller TRANE CH530. "SUCTION TEMPERATURE TOO HIGH alarm" in circuit 2. and I noticed that the discharge pressure in circuit 2 is lower compared to circuit 1. considering that both circuit are running. What is the possible cause of the alarm?



  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    18

    Re: Suction temperature too high alarm of trane cgam chiller

    Hi
    It could be a faulty sensor.
    Possibly a leak.
    Check your txv settings
    Good luck