    Jun 2014
    Scotland
    40
    38
    Mitsubishi electric suction pipe freezing
    I could some kind person help me please, I have a Mitsubishi puhz-rp125yha2.
    The suction pipe is frozen all the way into the compressor. I have check filters, fan motors and coils. All ok. Is this liquid coming back to the compressor or possible charge issue?
    Aug 2009
    Dartford
    34
    88
    15
    Re: Mitsubishi electric suction pipe freezing
    Check the expansion valve isn't fully opened
    Jun 2014
    Scotland
    40
    38
    How do you check that with the lev? Thanks
    Jun 2014
    Scotland
    40
    38
    No errors. Unit is working ok
    Oct 2007
    manchester
    5,639
    45
    is this the pipework within the condenser or the suction line from evap to condenser- is the lagging 13mm wall? you can get away with 9mm but if lagging is compressed with cableties or squashed on cable tray then that can cause sweating/frosting on suction line?- run it in test mode and view coil temp should be above freezing- otherwise ****ted up coil?
    Jun 2014
    Scotland
    40
    38
    Thanks guys much appreciated for the advice.
    Oct 2001
    Nottingham UK
    5,667
    Are the indoor filters clean?