Mitsubishi electric suction pipe freezing
I could some kind person help me please, I have a Mitsubishi puhz-rp125yha2.
The suction pipe is frozen all the way into the compressor. I have check filters, fan motors and coils. All ok. Is this liquid coming back to the compressor or possible charge issue?
Thanks
-
26-05-2016, 09:15 PM #2
Re: Mitsubishi electric suction pipe freezing
Check the expansion valve isn't fully opened
-
27-05-2016, 07:33 AM #3
Re: Mitsubishi electric suction pipe freezing
How do you check that with the lev? Thanks
-
30-05-2016, 09:27 AM #4
Re: Mitsubishi electric suction pipe freezing
No errors. Unit is working ok
-
30-05-2016, 08:42 PM #5
Re: Mitsubishi electric suction pipe freezing
is this the pipework within the condenser or the suction line from evap to condenser- is the lagging 13mm wall? you can get away with 9mm but if lagging is compressed with cableties or squashed on cable tray then that can cause sweating/frosting on suction line?- run it in test mode and view coil temp should be above freezing- otherwise ****ted up coil?
-
30-05-2016, 09:04 PM #6
Re: Mitsubishi electric suction pipe freezing
Thanks guys much appreciated for the advice.
-
01-06-2016, 06:50 PM #7
Re: Mitsubishi electric suction pipe freezing
Are the indoor filters clean?