    Carrier a/c short ccling



    Hi

    I have 2 Carrier air conditioners installed last year and they werenot cooling enough. I had noticed that every time I started them, the unit were short cycling 3 or 4 times before start operating normally.

    Recently the same technician came and added extra gas and added a dye to track any leaks. The units now are short cycling worst (operate for few seconds and stop) and I don't see any leak

    I have posted a video taken few days ago

    https://youtu.be/fG827G2k8Yc

    Could you give some ideas on what might be creating the problem ?

    Thaks



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Carrier a/c short ccling

    Unit is cycling on low pressure safety switch.

    Needs leak testing prior to recharging.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2014
    Location
    South Africa
    Age
    41
    Posts
    26
    Rep Power
    0

    Re: Carrier a/c short ccling

    Could it maybe be a blockage? suction line appearing low on charge, but unit short cycling on hp? If theres no leak that is?

  4. #4
    Join Date
    May 2016
    Location
    Canada
    Age
    58
    Posts
    2
    Rep Power
    0

    Re: Carrier a/c short ccling

    Thanks for your answers. I do suspect it is some sort of blockage. I noticed the technician was getting high pressure when trying to add refrigerant during last visit and had to allow some time to let it flow. He said it was due to high viscosity of the dye he was using to find leaks. He said it had some oil which was good for the compressor.

    If this is a blockage, what would be the basic steps to fix it? Having same issue in both units makes me suspect of some error during installation. I haven't changed company to keep warranty but I'm loosing confidence on these guys
    Last edited by Baezf; 23-05-2016 at 09:10 PM.

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Carrier a/c short ccling

    You can get the same symptoms on High pressure switch when the switch is set for 'Auto reset' rather than manual reset.

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Carrier a/c short ccling

    Don't let it run like that, cycling on and off will kill a compressor in no time, they should only start 10 times an hour.

    Don't know what make compressors your units have, but copeland had a problem with a rust proofing chemical they used during manufacturing reacting once the system was running and blocking up the expansion valve, causing low suction pressures. To an uneducated technician a low suction pressure will look like a leak.... Just an idea.
    Mostly found in Oxfordshire, UK :)

  7. #7
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Carrier a/c short ccling

    Talk to your Carrier supplier, and get it sorted out under warranty, Carrier should send a competent service technician to fix it.

  8. #8
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Carrier a/c short ccling

    Quote Originally Posted by Baezf View Post
    Thanks for your answers. I do suspect it is some sort of blockage. I noticed the technician was getting high pressure when trying to add refrigerant during last visit and had to allow some time to let it flow. He said it was due to high viscosity of the dye he was using to find leaks. He said it had some oil which was good for the compressor.

    If this is a blockage, what would be the basic steps to fix it? Having same issue in both units makes me suspect of some error during installation. I haven't changed company to keep warranty but I'm loosing confidence on these guys
    I have lost faith in them already :-)

  9. #9
    Join Date
    Feb 2016
    Location
    Uk
    Age
    48
    Posts
    48
    Rep Power
    0

    Re: Carrier a/c short ccling

    Find your expansion valve if it is freezing up strait away on start up then it is starving the condenser and you have moisture in the system. To fix this pump down install filter dryer and vac out