    Hall Screw Oil Return Issues



    Hi, I am having issues with a Hall Screw 2020 running on Ammonia. When compressor is running unloaded oil level in seperator is good, as soon as compressor starts loading up oil level in sperator starts dropping off untill compressor trips on low oil level fault. Once compressor is switched off the oil returns to seperator. the oil seems to be held up in compressor for some reason, any ideas?



  2. #2
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,035
    Blog Entries
    4
    Rep Power
    31

    Re: Hall Screw Oil Return Issues

    Do you have a picture of the compressor package/Oil separator?

    I see this on some oil separators, when the compressor is on low load there will be oil on the max mark, but once it's running on full capacity the oil level will drop significantly.

    Also a wet suction or rapid changes in the capacity can make the oil foam up and make the level switch drop, even though you have enough oil, especially on vertical oil separators.
    -Cheers-

    Tycho

  3. #3
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14

    Re: Hall Screw Oil Return Issues

    send some photos.
    probably problem with pressure equation between crankcase and separator.
    for a particular reason the oil is transferred violently towards the crankcase when the demand for cooling capacity is high and the compressor pumps to a high degree.

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Hall Screw Oil Return Issues

    Have heard of a few where internal ball bearing check valve in discharge has fallen out.
    Held in by circlip or similar
    Observed poor performance & little ice on suction line

  5. #5
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Hall Screw Oil Return Issues

    Discharge pipe go high and without oil traps? )))

  6. #6
    Join Date
    May 2016
    Location
    New Zealand
    Age
    38
    Posts
    5
    Rep Power
    0

    Re: Hall Screw Oil Return Issues

    I will try get some photos over the next day or so. The capacity on this compressor is normally fairly stable as this is a holding room, not used for pulling down product. We have two identical compressor skids on this site, but only one seems to be having this problem.

  7. #7
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,035
    Blog Entries
    4
    Rep Power
    31

    Re: Hall Screw Oil Return Issues

    Quote Originally Posted by JP85 View Post
    I will try get some photos over the next day or so. The capacity on this compressor is normally fairly stable as this is a holding room, not used for pulling down product. We have two identical compressor skids on this site, but only one seems to be having this problem.
    Followup questions:
    Are the two compressor units connected on the same system (common suction and discharge),
    -are these two compressors running on the same system?
    -are the compressors running at the same time?
    -are they connected to a common suction and discharge line?
    -if they are not on the same system, are there any differences in suction pressure? (higher suction pressure on the problem unit?)
    -is this something that has developed, or has it been a problem since it was installed?
    -Have you tried charging oil while it was running, to raise the oil level during operation?


    Looking forward to hearing from you
    -Cheers-

    Tycho