Results 1 to 4 of 4
  1. #1
    Join Date
    May 2016
    Location
    UAE
    Age
    32
    Posts
    2
    Rep Power
    0

    Smile 30GX carrier chiller



    Good afternoon every body..
    I have problem with 30Gx carrier chiller
    It have two circuit B & A1, A2.
    There's one alarm coming..
    The code number is 19, it's refer to oil transducer for circuit A2 but we changed new one,
    still the same alarm coming.
    Please can you help me urgently.

    Thanks



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: 30GX carrier chiller

    I thought code 19 referred to oil temperature.

    Have you checked the crankcase heater is working?
    Unit will not start with cold oil.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2016
    Location
    UAE
    Age
    32
    Posts
    2
    Rep Power
    0

    Re: 30GX carrier chiller

    I checked the code alarm..
    19 referred to oil transducer
    Also crankcase heater working..

  4. #4
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: 30GX carrier chiller

    Assuming you changed the right transducer.Check your plug connection at the board make sure wires are tight in plug also check 5vdc output at plug.
    Could be cable , plug at board or maybe board but I would go for loose connection at plug at the board.
    Gibbo
    Last edited by Gibbo; 15-05-2016 at 06:48 PM.