Results 1 to 3 of 3
  1. #1
    Join Date
    Jun 2010
    Location
    USA
    Age
    38
    Posts
    12
    Rep Power
    0

    compressor capacity question



    Hello,

    I got a single door kegerator that originally had a 1/6 hp 450 btu r12 compressor.
    Coldparts just sent me a 1/8 hp 400 btu r134a compressor. I will be charging it with r134a.
    Should I send the compressor back or not. I'm thinking I will lose some capacity just from switching to r134a. Will the cap tube be sized correctly? Or should I change the cap tube based on the supco or JB sizing chart?

    This unit will be for personal use so I thought I would save some bucks, and I ordered the compressor from coldparts.com

    Any help would be greatly appreciated.

    Thanks,
    Jake



  2. #2
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: compressor capacity question

    Faulty fractional Horse Power compressors should be replaced with a suitable match, or at least within 5% +-.
    Get on the blower and ask why they sent you a smaller Pot.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  3. #3
    Join Date
    May 2016
    Location
    SPAIN
    Age
    40
    Posts
    35
    Rep Power
    0

    Re: compressor capacity question

    Can you check the capacity that your new compressor gives for R12? I am sure you know, but depending on the refrigerant you use your compressor gives different capacities. Maybe your new compressor gives the same capacity for R12?