I just want to check I'm right here. I have had a split system heat pump installed, at the condensing unit, both refrigerant lines are lagged individually, but where they run inside the building, hidden from view behind some panelling, both lines have been pulled through the same length of armourflex, as in both the copper lines touch one another.

I dont think this is right, can anyone confirm?