Thread: pool heat pump

  1. #1
    Join Date
    Sep 2005
    Location
    spain
    Age
    53
    Posts
    54
    Rep Power
    0

    pool heat pump



    Hi I am trying to sort out other peoples **** ups out as usual and need help on this one . its a air energy 550 ti3 heat pump on 407c and only giving 2c diferance the coil is not swetting and pressure is +10c suction . i do know that the water throug put is about 1/3 more than it should be so poss over condencing? air temp is about 24c today as well. in sunny costa del sol. help?????



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: pool heat pump

    And what is the problem?

  3. #3
    Join Date
    Sep 2005
    Location
    spain
    Age
    53
    Posts
    54
    Rep Power
    0

    Re: pool heat pump

    the unit can be on for 4days and only rais water by 2c and thats in summer . in winter the coil frezzes up.

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: pool heat pump

    It's normal in winter coils freezes, especially if on the condensing side the pool water is cold. Untill water warms up, there's no way to keep condensing pressure high enough.
    What is the SH and SC? How much the water warms up between in and out of the condenser (not the pool, just the condenser).

    Have you tried to calculate the heat loss from the pool to the actual heating capacity of the heat pump?

  5. #5
    Join Date
    Jan 2006
    Location
    Lanzarote
    Posts
    13
    Rep Power
    0

    Re: pool heat pump

    Hi Coolflow

    Water temp rise is not a good performance indicator, its the air temp difference accross the air Hx that matters. To measure this you will need two thermometers ideally, one in the ambient air and one in the air Hx discharge but make sure the fan & Hx are clean.

    Armed with the temp diff you should be able to calculate the heat pickup providing you know the fan performance, if you don't, contact the heat pump manufacturer who should be able to give you this info. If you have the book supplied with the pump the target performance may be listed. On pool systems the air temp diff is more reliable than water diff because its not system specific and its also greater, probably around 4dC. However you will need to know both wet & dry bulb temperatures to get an accurate calculation of the heat recovered. You will also need to know the electrical energy input if you are trying to evaluate the COP or actual performance. However do not use rated amps v measured amps as the yardstick for establishing if the pump is performing properly.

    Performance is quite sensitive to ambiant air temperature and actual pool water temperature, the cooler the air and the hotter the pool the less recovery you will get from the air and the lower the COP will be.

    Hope this helps, Good luck, LanzaCarlos

    Quote Originally Posted by coolflow
    Hi I am trying to sort out other peoples **** ups out as usual and need help on this one . its a air energy 550 ti3 heat pump on 407c and only giving 2c diferance the coil is not swetting and pressure is +10c suction . i do know that the water throug put is about 1/3 more than it should be so poss over condencing? air temp is about 24c today as well. in sunny costa del sol. help?????

  6. #6
    Join Date
    Sep 2005
    Location
    spain
    Age
    53
    Posts
    54
    Rep Power
    0

    Re: pool heat pump

    many thanks for all help will see later this week

  7. #7
    Join Date
    May 2006
    Location
    Canberra
    Age
    74
    Posts
    7
    Rep Power
    0

    Re: pool heat pump

    [quote=NoNickName]It's normal in winter coils freezes,
    especially if on the condensing side the pool water is cold. Untill water warms up, there's no way to keep condensing pressure high enough.
    What is the SH and SC? How much the water warms up between in and out of the condenser (not the pool, just the condenser).

    The air temperature is 24 C, the condensor can not freeze-up because hot gas is in it. You better read the post more carefully before confusing somebody.

  8. #8
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: pool heat pump

    [QUOTE=curious123]
    Quote Originally Posted by NoNickName
    It's normal in winter coils freezes,
    especially if on the condensing side the pool water is cold. Untill water warms up, there's no way to keep condensing pressure high enough.
    What is the SH and SC? How much the water warms up between in and out of the condenser (not the pool, just the condenser).

    The air temperature is 24 C, the condensor can not freeze-up because hot gas is in it. You better read the post more carefully before confusing somebody.
    Better you waited before answering. In winter the condensing coil becomes the evaporator. Like in all reversible heat pumps.
    In fact, the poster says the coil does not sweat, this means that the coil doesn't have hot gas in it.

  9. #9
    Join Date
    May 2006
    Location
    Canberra
    Age
    74
    Posts
    7
    Rep Power
    0

    Re: pool heat pump

    How do you make a coil sweat with hot gas please?

Similar Threads

  1. New Heat Pump Forum
    By Argus in forum Heat Pumps
    Replies: 17
    Last Post: 10-04-2010, 09:12 AM
  2. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  3. Heatstar swimming pool heat pump
    By Latte in forum Trouble Shooting
    Replies: 9
    Last Post: 28-06-2007, 06:15 PM
  4. Rebuild air2air heat pump
    By stalker in forum Technical Speculations
    Replies: 3
    Last Post: 02-11-2006, 10:10 AM
  5. heat pump capacity adjust
    By Lc_shi in forum Fundamentals
    Replies: 5
    Last Post: 14-02-2006, 07:32 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •