Thread: thermo king SL200e 71 & 111
-
04-05-2016, 09:48 PM #1
thermo king SL200e 71 & 111
How are you guys
i have thermo king sl200e whit thermoguard vi b
alarm code 71
I was trying to rest to zero
Changing figures inadvertently H4L and HR4
now alarm code is 71 and 111
how to fix it pls
-
10-05-2016, 03:26 AM #2
Re: thermo king SL200e 71 & 111
Change H4T (hourmeter 4 type) to 0 (not active) to completely disable the hourmeter.
H4L is hourmeter limit when it will trigger code 71
HR4 is hourmeter accumulated hours. Scroll this down to zero to reset.
Clear alarm 71 in guarded access.
-
13-05-2016, 02:26 PM #3
Re: thermo king SL200e 71 & 111
thanks dear
what abute alarm code 50
i SET CLOCK but After re-opening the unit back again
-
13-05-2016, 08:54 PM #4
-
13-05-2016, 09:31 PM #5
Re: thermo king SL200e 71 & 111
change event log to none in super guarded access.
tk and clear button when your at the sbit screen will get your there. change to no
really simple on UP-VI
-
14-05-2016, 05:49 AM #6
-
17-05-2016, 01:26 PM #7
Re: thermo king SL200e 71 & 111
just googled it you have the TG VI
-
17-05-2016, 11:52 PM #8
-
18-05-2016, 05:44 PM #9
-
18-05-2016, 07:23 PM #10
Re: thermo king SL200e 71 & 111
111 is unit not configured correctly.
If the unit is configured correctly replacing the eprom is the fix. 40-896 is the part number revision 1091.
This is a known issue on the SL200
Changing the hourmeter settings won't cause a code 111.