    Climaveneta NECS/B 0804. Flow rate? Or Manual



    I have a Climaveneta NECS/B 0804. Could someone please tell me what the pressure drop required across the Evaporator should be for chilled water flow??

    Or better still does someone have the manual with these in?

    Thanks very much



  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Climaveneta NECS/B 0804. Flow rate? Or Manual

    Hi
    your wanted pressure drop is approx. 5.5 to 6 meters on the evaporator .
    and 34-36 m3h of water flow.
    good luck