Results 1 to 7 of 7
  1. #1
    Join Date
    Apr 2016
    Location
    Lietuva
    Age
    32
    Posts
    4
    Rep Power
    0

    Fujitsu VRF II inverter compressor lock



    Hi, everyone

    Unit consists of 1 inverter compressor, and 2 on/off compressors, client used to hire another company (fujitsu dealers in my country fml), they have changed 9 compressors in ~2 years.

    Compressor makes a ticking sound for few seconds, but doesn't start up. Replaced inverter board, but that didn't help either.

    We took refrigerant samples and in the lab we found that there was a lot of non condensibles (air) in the system, piping diameters and lenght are ok, so we pumped down the refrigerant, changed a compressor,, filled system with nitrogen, vacuumed and put a fresh r410A in the system, all according to unit needs and pipe lenghts after a few days and tried the new baby.
    Compressor worked well... for a minute. Then same symptoms happened. we checked pipes for clogging, everything seems to be fine.

    Masters, any ideas why did the compressor was locked again after ~1 minute of work?



  2. #2
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14

    Re: Fujitsu VRF II inverter compressor lock

    how about checking the power and Hertz?

  3. #3
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Fujitsu VRF II inverter compressor lock

    Ahaha, I dont understand how they can kill twin rotor invertor)))
    You need to clean all pipes from oil.
    Next you need find someone with Service Tool, and find why they dead.
    High discharge temperature and injection i think.
    Someone fiil pipes with nitrogen anothers open valves without vacuumation)

  4. #4
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Fujitsu VRF II inverter compressor lock

    Hi,

    Compressor configuration like that would be V series. VII used one inverter and one fixed speed unless your region had something special?

    Inverter circuit needs testing as already said, any fault codes, something broken up and getting sucked into compressor. Do fixed speeds run when contactor pressed in (if V series then plenty of compressor issues in the early days esp with master and slave setup), power and connections through noise filter, IPM boards, capacitors and external resistors alright, cables to compressors, main supply and neutral.
    Has Fujitsu looked at it or just an AC contractor?

    If compressor is locked again that quick then you need to chop it open and see what has got sucked inside. Perhaps check the one you've taken out first and make sure customer has a fat wallet which they don't mind emptying, good luck!

    Andy.
    Health and safety first..........unless I'm in a hurry.

  5. #5
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,035
    Blog Entries
    4
    Rep Power
    31

    Re: Fujitsu VRF II inverter compressor lock

    Never mind, thought it was something else, sorry
    Last edited by Tycho; 20-04-2016 at 08:49 PM.
    -Cheers-

    Tycho

  6. #6
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Fujitsu VRF II inverter compressor lock

    Airstage V dont check of alternation of phases.
    If have confused with power supply or have confused with wires to the compressor after the IPM - compressor will jam.
    Last edited by RusBuka; 21-04-2016 at 07:59 AM.

  7. #7
    Join Date
    Apr 2016
    Location
    Lietuva
    Age
    32
    Posts
    4
    Rep Power
    0

    Re: Fujitsu VRF II inverter compressor lock

    As i said, fujitsu in our country are not really the best people to ask for help. They have been here lots of times, and they have changed 9(!!!) compressors in a year. And thats it they didnt offer any explaination for user or anything.

    On the electric side everything seems to be ok, tested ipm board on another unit, works fine.
    We cut open compressor, doesn't seem tragic, just some copper dust, although not much.
    Could even a small amount of debris cause this?
    Is it possible that power module sometimes switch phases and as RusBuka said - jam a compressor?

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •