    Capacitor Selection



    Ok so i know how to read a capacitors mfd but my question is multi fold regarding a formula i came across. In one video the guy said to measure a capacitor under load take the amps of the wire leading to the compressor start multiply by 2650 and divide by the vac reading on the common to start of the cap and it will give you the actual capacitance of the cap. Another website used the exact same formula except for the number 2650, they used 2652 as the number and said that is the formula to check what cap a motor actually needs.

    My questions.

    1) Is there any truth to the second formula? Bearing in mind a capacitor has to cause a 90 deg phase shift, is a simple formula accurate to determine what size cap is needed by a motor if you dont have a reliable source to work from ie a manufacturers rating etc.

    2) If the first formula is accurate then what would happen if the compressor was drawing more amperage than it should ie from an overcharge or similar factors affecting the compressor amp draw. Not that i wouldnt check these things but for the novice out there who would rely on this i could foresee this formula as a problem?

    3) From personal experience ive come across techs using the +- 5% rule a bit too lenient. first cap being a 35uf, tech replaces it with a 40 because he doesnt have a 30 or 35 in the van and he is 50km away from a supply shop. Next guy does the same thing, only putting the next size up before you know it the compressor has failed due to this problem. Is there a formula to determine what a motor needs cap wise?



  2. #2
    Join Date
    Aug 2014
    Location
    South Africa
    Age
    40
    Posts
    26
    Rep Power
    0

    Re: Capacitor Selection

    50 viewers dont all jump at once and damage the pace maker to respond

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Capacitor Selection

    I was one of the 50 but didn't know the answer to you question

    I fit the size capacitor the motor data plate calls for, the +/- 5% is the manufacturing tolerance for the capacitor, not the motor, nor for the use of techs too lazy to get the correct part.
    Mostly found in Oxfordshire, UK :)

  4. #4
    Join Date
    Aug 2014
    Location
    South Africa
    Age
    40
    Posts
    26
    Rep Power
    0

    Re: Capacitor Selection

    Quote Originally Posted by monkey spanners View Post
    I was one of the 50 but didn't know the answer to you question

    I fit the size capacitor the motor data plate calls for, the +/- 5% is the manufacturing tolerance for the capacitor, not the motor, nor for the use of techs too lazy to get the correct part.
    Thanks for the reply monkeyspanners, i checked up it seems you can only do this with an oscilloscope.

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Capacitor Selection

    I am aware of the vector shift for higher starting torque using start capacitors, and the higher voltage requirement for permanent run capacitors . Short ot testing capacitors with Fluke that is extent of it for me. Somewhere I have description for paralleling and series up caps.
    Generally have enough problems with the refrigeration side of things, hence this is a refrigeration forum! But can understand if vector shift is too high with wrong capacitor the motor will stall overload and then fail.

  6. #6
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: Capacitor Selection

    Blew one up once!pretty darn scary believe me.

  7. #7
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Capacitor Selection

    Yes and I have been whacked by the odd one discharging into my pinkies , geez it hurt

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •